Skip to content

Quick Switchgear + PCS Seamless Switching Solution (<20ms)

Document Date: 2026-09-07 Issuing Department: Hoenergy — Overseas Business Division, Technology Center Prepared by: Alvin

§0 30-Second Briefing (Executive Summary)

Q. Core Customer Question: How can an energy storage system keep the load powered during a grid outage, and how fast can the switching time be?

🔴 A. Key Conclusions

Item Conclusion
Switching Time With a 125 kW PCS (AC400V), switching time ≤20 ms; with a 215 kW PCS (AC800V), switching time ≤30 ms
Core Components Empower EQS series fast transfer switch + EPCS125-AM(-F) (VG version) or EPCS215-AM-HX (VG version)
Switching Principle EQS static switch + PCS built-in VSG algorithm for phase-lock synchronization; mechanical opening and electrical switching are completed within the same timing window
Control Method VG voltage sampling + DIO dry contacts (DO4/DI3) + (CAN weak communication, transmission distance <20 m)
Parallel Capacity A single EQS supports 1–10 PCS units in parallel (when the number of paralleled PCS units exceeds 6, CAN weak communication is required to transmit off-grid information)

B. Three Red Lines at a Glance

# Red Line
R1 EQS switchover ≤20 ms is only valid when paired with a 125 kW PCS; for 215 kW it is ≤30 ms
R2 EQS-2000R, EQS-2600R, and EQS-4000R are 3P without an N1 terminal; for TN-C/TN-S systems, a 4P model must be selected or an external neutral-point treatment must be provided
R3 VSG paralleling is limited to 10~12 units; any number above this must be grouped

See Appendix A for the complete list of red lines R1–R10.


§1 Product Portfolio (Hoenergy D-Cube + EVALUE EQS)

1.1 Product Portfolio Overview

Product Model Role Key Parameters
Fast Transfer Switch EQS Series (6 models) Millisecond-level mechanical switching between grid/PCS ≤20 ms (30 ms) / 99.97% efficiency
Energy Storage Integrated Cabinet D-Cube-S125/261-EU (VG) Store electrical energy and provide backup power when the grid is lost 125 kW / 125 kWh / AC 400 V
Energy Storage Integrated Cabinet D-Cube-A Series (VG) +261D Store electrical energy and provide backup power when the grid is lost N x 125 kW / N x 261 kWh / AC 400 V
Energy Storage Integrated Cabinet D-Cube-F215/418 (VG) Store electrical energy and provide backup power when the grid is lost 215 kW / 418 kWh / AC 800 V

Why is there a VG version?

The PCS used together with the EQS is a special PCS version. Compared with the standard version, the hardware has an additional VG voltage sampling terminal, and the software program uses the VSG version.

ScreenShot_2026-09-17_193331_159
ScreenShot_2026-09-17_193344_375

1.2 Enjiu EQS Series (6 Models, Full Current Range)

Image111
Model Rated Current Poles 400 V Capacity 800 V Capacity Switching Time Efficiency Weight
EQS-500(4)R 500 A 4P 346 kVA 693 kVA ≤20 ms 99.95% 10 kg
EQS-750(4)R 750 A 4P 520 kVA 1040 kVA ≤20 ms 99.97% 15 kg
EQS-1300(4)R 1300 A 4P 900 kVA 1800 kVA ≤20 ms 99.97% 25 kg
EQS-2000R 2000 A 3P 1385 kVA 2770 kVA ≤20 ms 99.97% 35 kg
EQS-2600R 2600 A 3P 1800 kVA 3600 kVA ≤20 ms 99.97% 42 kg
EQS-4000R 4000 A 3P 2770 kVA 5540 kVA ≤20 ms 99.97% 60 kg

⚠️ Paired with a 125 kW PCS (AC400 V), the switching time is ≤20 ms; paired with a 215 kW PCS (AC800 V), the switching time is ≤30 ms.

EQS Technical Specifications: EQS Product Datasheet

Item Value
Voltage Range 400-1140 VAC
Power Supply 220-270 VAC (Independent Supply)
Control Method DIO Digital (DO4+/DO4-, DI3+/DI3-)
Operating Temperature -30 ℃ ~ 50 ℃
Storage Temperature -45 ℃ ~ 70 ℃
Relative Humidity 0-95% RH, non-condensing
Cooling Method Natural Cooling / Intelligent Air Cooling
Protection Rating IP00
Wiring Method Three-Phase Three-Wire / Three-Phase Four-Wire
Altitude 4000 m (>2000 m, derate by 1% per 100 m)
Service Life 100,000 - 1,000,000 cycles (depending on model)

1.3 EQS Product Dimensions and Installation

1.3.1 Product Dimensions

5004R
7504R
13004R
2000R
2600R
4000R

1.3.2 Installation Method

✅ Correct installation method: Mount vertically on the wall, perpendicular to the ground

CORRECT

❌ Incorrect installation method: Installed parallel to the ground

INCORRECT

§2 EQS Selection (by 125 kW PCS unit count × N)

2.1 Selection General Principle: Dual-Condition Determines

Core formula:

EQS apparent capacity ≥ PCS maximum charging power + load usage power (must be satisfied under any operating condition)

Operating condition Description EQS flowing apparent power
Single condition (load only) PCS discharges to power the load, battery has sufficient charge S_load = P_load / cosφ
Dual condition (charging + load simultaneously, the most stringent) PCS charges the battery while simultaneously supplying power to the load S_total = (P_charge + P_load) / cosφ

Why the dual condition is the determining condition:

  1. Charging current path: Grid → EQS → PCS → Battery (passes through the EQS)
  2. Load current path: Grid → EQS → Load (passes through the EQS)
  3. The two currents algebraically superimpose at the EQS (same direction)
  4. When the charging period (energy storage replenishment during off-peak electricity price periods) overlaps with a high-load period → EQS flow reaches its peak

Charging power assumption (typical operating conditions):

Charging strategy Charging power of a single PCS
Full-power charging (default) 125 kW (same power as discharging)
Limited-power charging (conservative) 100 kW
Off-peak charging (recommended) Different time periods, the peak of a single unit drops to 50–80 kW

2.2 Load Requirements (EnJoy PCS Off-Grid Load Capacity)

Regarding the requirements of VSG mode on load type (core clarification):

Although this solution switches to VSG mode when off-grid, just like the traditional VF (constant voltage and constant frequency) mode, VSG mode also has requirements on load type. The risk of switching failure or load-carrying failure still exists. VSG is not a "universal cure-all". In essence, both are grid-forming modes, and the off-grid principle is the same.

The three scenarios that VSG truly improves are:

  1. Motor starting — Virtual inertia J simulates rotor energy storage, capable of absorbing 6-8 times the inrush current without causing frequency collapse (in VF mode, the inrush current directly causes frequency drop);
  2. Transformer magnetizing inrush current — Virtual damping D suppresses transient oscillations;
  3. Multi-machine parallel power sharing — More stable based on virtual impedance.

Loads that cannot be applied or require special evaluation (same restrictions as VF mode):

  1. Single-phase high-power equipment (>30% of total power) requires a DyN11 isolation transformer;
  2. Direct starting of large motors (>10 kW) requires soft starting or star-delta step-down;
  3. Non-linear loads (inverters, rectifiers, THD > 8%) require active power filter APF;
  4. Impact loads (spot welders, arc furnaces) require PCS capacity amplification by 1.5-2 times;
  5. Oversized capacitor compensation cabinet (>30% PCS capacity) may cause self-excited oscillation;
  6. Parallel operation with diesel generators/PV requires synchronous verification and coordinated control.

Tip

Strong recommendation: Complete the collection of customer load list (power, type, starting method) before project initiation.

2.2 Single-Condition Selection Table (Load Only, Battery Not Charging)

Assumptions:

  • cosφ = 0.8 (typical for industrial and commercial loads before compensation; typically 0.90–0.98 after compensation)
  • In single-condition operation, the PCS only discharges, with sufficient battery state of charge
  • Maximum load under single condition P_load = N × 100 kW (80% of PCS capacity, reserving a 20% PCS capacity margin, an engineering-conservative assumption)
  • The full-load rating per unit (125 kW/unit) is covered in §2.9 Benchmark Case (extreme condition)
PCS Units N Total PCS Capacity Maximum Single-Condition Load P_load S_load Apparent Power (cosφ 0.8) Recommended EQS EQS 400V Capacity Margin
1 125 kW 100 kW 125 kVA EQS-500(4)R 346 kVA 277%
2 250 kW 200 kW 250 kVA EQS-500(4)R 346 kVA 138%
3 375 kW 300 kW 375 kVA EQS-750(4)R 520 kVA 139%
4 500 kW 400 kW 500 kVA EQS-750(4)R 520 kVA 104%
5 625 kW 500 kW 625 kVA EQS-1300(4)R 900 kVA 144%
6 750 kW 600 kW 750 kVA EQS-1300(4)R 900 kVA 120%
7 875 kW 700 kW 875 kVA EQS-1300(4)R 900 kVA 103%
8 1.0 MW 800 kW 1000 kVA EQS-2000R 1385 kVA 139%
9 1.125 MW 900 kW 1125 kVA EQS-2000R 1385 kVA 123%
10 1.25 MW 1000 kW 1250 kVA EQS-2000R 1385 kVA 111%

Note

In engineering practice, it is easy to assume cosφ = 1.0 (resistive load) and select EQS-1300(4)R (900 kVA), but with actual industrial and commercial loads at cosφ ≈ 0.8, 1000 kVA exceeds 900 kVA and will cause overload tripping. Selection must be rigorously verified using the formula in §2.8: S_EQS = P_load / cosφ. cosφ must not be assumed to be 1.0.

2.3 Dual-Mode Selection Table (Charging + Load Simultaneously, Most Conservative)

Assumptions (full-power charging, matched to PCS rating):

  • Single PCS charging power = 125 kW (full power, same as PCS discharging power)
  • Total charging power = N × 125 kW
  • Maximum single-mode load P_load = N × 100 kW (80% of PCS capacity, consistent with the engineering convention in §2.2)
  • cosφ default 0.8 (typical commercial/industrial)

Source of the full-power charging assumption: The EMS of an energy storage project generally does not limit the charging power (charging periods have low electricity prices, encouraging more charging). The conservative assumption uses full power of 125 kW per unit, forming a contrast with the power-limiting scheme (A) in §6.5.

> User full-load convention (P_load = N × 125 kW) is shown in the benchmark case in §6.9 (1250+1250=2500 kW → EQS-4000R, red line R7), which is more conservative than this table.

PCS Quantity N Charging Power N×125 Single-Mode Load P_load Dual-Mode Total Power P_charge + P_load S_total (cosφ 0.8) Recommended EQS (Dual-Mode) 400V Capacity Margin
1 125 kW 100 kW 225 kW 281 kVA EQS-500(4)R 346 kVA 123%
2 250 kW 200 kW 450 kW 563 kVA EQS-750(4)R 520 kVA 92% ⚠️ Critical
3 375 kW 300 kW 675 kW 844 kVA EQS-1300(4)R 900 kVA 107%
4 500 kW 400 kW 900 kW 1125 kVA EQS-2000R 1385 kVA 123%
5 625 kW 500 kW 1125 kW 1406 kVA EQS-2000R 1385 kVA 99% ⚠️ Critical
6 750 kW 600 kW 1350 kW 1688 kVA EQS-2600R 1800 kVA 107%
7 875 kW 700 kW 1575 kW 1969 kVA EQS-2600R 1800 kVA 91% ⚠️
8 1000 kW 800 kW 1800 kW 2250 kVA EQS-2600R 1800 kVA 80% ⚠️
9 1125 kW 900 kW 2025 kW 2531 kVA EQS-4000R 2770 kVA 109%
10 1250 kW 1000 kW 2250 kW 2813 kVA EQS-4000R 2770 kVA 99% ⚠️ Critical

⚠️ N=10 Engineering Convention (80% load):

10 PCS × 125 kW charging + 10 PCS × 100 kW load = 1250 + 1000 = 2250 kW dual-mode total power Apparent power = 2250 / cosφ 0.8 = 2813 kVA → EQS-4000R (4000 A / 3P / 2770 kVA) must be selected, but 2813 kVA > 2770 kVA, the EQS-4000R capacity may actually be insufficient! → cosφ must be raised to ≥ 0.83

⚠️ Critical Warning: Under the full-power charging assumption, more than 4 PCS units approach the upper limit of EQS-2000R, and more than 6 units require upsizing to EQS-2600R/4000R.

2.4 Single-Condition vs Dual-Condition Sizing Comparison (Key Insights)

PCS Quantity N /125kW Single-Condition EQS Dual-Condition EQS Upgrade Reason
1 EQS-500(4)R EQS-500(4)R Same tier (sufficient headroom)
2 EQS-500(4)R EQS-750(4)R +1 tier (charging + load stacking exceeds 346 kVA)
3 EQS-750(4)R EQS-1300(4)R +1 tier
4 EQS-750(4)R EQS-2000R +2 tiers (skip 1300, jump straight to 2000)
5 EQS-1300(4)R EQS-2000R +1 tier
6 EQS-1300(4)R EQS-2000R +1 tier ⚠️ Critical (92%)
7 EQS-1300(4)R EQS-2600R +2 tiers
8 EQS-2000R EQS-2600R +1 tier
9 EQS-2000R EQS-2600R +1 tier
10 EQS-2000R EQS-4000R +2 tiers

Key Insights:

  • Dual-condition requires a higher-tier EQS than single-condition, with an upgrade magnitude of 1–2 tiers;
  • N ≤ 3 units: The difference between single and dual conditions is small; EQS-500/750 can both cover the requirement;
  • N = 4–6 units: Dual-condition goes up 1 tier; EQS-2000R is the maximum capacity that can be covered within the current specification limit;
  • N ≥ 7 units: Dual-condition requires EQS-2600R/4000R.

2.5 Engineering Trade-Off Solutions (Dual-Condition Coverage with N ≥ 7 PCS Units)

Option Description Trade-Off
A. Limit Charging Power EMS limits charging per PCS unit to ≤ 50-80 kW Total charging time extended by 2-3x, but the dual-condition power is significantly reduced
B. Off-Peak Charging Avoid load peaks during charging periods (e.g., charge at night 23:00-05:00) Requires EMS time-of-use strategy alignment, fits well with time-of-use tariff policies
C. Expand EQS Selection Directly select EQS-2600R/4000R when N ≥ 7 units Capacity per EQS unit is increased

Option A Detailed Calculation (Limit Charging Power ≤ 50 kW per unit):

PCS Quantity N Charging Power N×50 Single-Condition Load P_load Dual-Condition Total Power S_total (cosφ 0.8) Recommended EQS 400V Capacity Margin
7 350 kW 700 kW 1050 kW 1313 kVA EQS-2000R 1385 kVA 105% ✅
8 400 kW 800 kW 1200 kW 1500 kVA EQS-2000R 1385 kVA 92% ⚠️ Critical
9 450 kW 900 kW 1350 kW 1688 kVA EQS-2600R 1800 kVA 107% ✅ (Requires expanded specification)
10 500 kW 1000 kW 1500 kW 1875 kVA EQS-2600R 1800 kVA 96% ⚠️ Critical

Option B Off-Peak Charging (Recommended):

  • Off-peak periods: Low electricity price → Charging periods
  • Peak periods: High electricity price → Discharge to support load + no charging

With off-peak charging, charging and load periods are naturally staggered, and the dual-condition scenario becomes a single-condition coverage. This is the most commonly used approach for commercial and industrial energy storage.

Option C Expand EQS Selection:

Exceed the project specification upper limit and expand to EQS-2600R (2600 A) or EQS-4000R (4000 A).

  • EQS-2600R 400V capacity: 1800 kVA
  • EQS-4000R 400V capacity: 2770 kVA
  • Suitable for 10 PCS units at full-power charging scenario

2.6 AC 800V High-Voltage Platform Selection

  • If the customer adopts an 800V platform (paired with ENJOY 215 kW PCS), the single-condition EQS capacity is doubled (at the same current level), and the switching time is reduced from ≤20 ms to ≤30 ms.
800V Platform Capacity Total Power Recommended EQS (Single-Condition) 800V Capacity Margin
215 kW × 1 215 kW EQS-500(4)R 693 kVA 322% ✅
215 kW × 2 430 kW EQS-500(4)R 693 kVA 161% ✅
215 kW × 3 645 kW EQS-750(4)R 1040 kVA 161% ✅
215 kW × 4 860 kW EQS-750(4)R 1040 kVA 120% ✅
215 kW × 5 1075 kW EQS-1300(4)R 1800 kVA 167% ✅
215 kW × 6 1290 kW EQS-1300(4)R 1800 kVA 140% ✅
215 kW × 7 1505 kW EQS-1300(4)R 1800 kVA 120% ✅
215 kW × 8 1720 kW EQS-1300(4)R 1800 kVA 105% ⚠️ Critical
215 kW × 9 1935 kW EQS-2000R 2770 kVA 143% ✅
215 kW × 10 2150 kW EQS-2000R 2770 kVA 129% ✅

Pattern: 1-2 → EQS-500 | 3-4 → EQS-750 | 5-8 → EQS-1300 | 9-10 → EQS-2000

Tip

⚠️ N=8 Engineering Note: A margin of 105% means only a 5% capacity headroom (current 1241 A vs. EQS-1300 rated 1300 A = 95.5%). According to the engineering requirement of a ≥10% safety margin, upgrading to EQS-2000R is recommended (143% margin, 61% headroom). If the 5% boundary risk is acceptable, EQS-1300(4)R may be retained.

2.7 Selection Decision Tree

ScreenShot_2026-09-18_134941_593

Typical Selection Result Examples:

Customer Load Charging Strategy Single-Cabinet Selection EQS
500 kW Off-peak charging D-Cube-S261 × 4 (1044 kWh) EQS-750(4)R
500 kW Dual-mode operation D-Cube-S261 × 4 (1044 kWh) EQS-2000R
1000 kW Off-peak charging D-Cube-A500 × 2 + D-Cube-261D × 8 (2.088 MWh) EQS-2000R
1000 kW Dual-mode operation D-Cube-A500 × 2 + D-Cube-261D × 8 (2.088 MWh) EQS-4000R
1250 kW backup power (10 units) Off-peak charging D-Cube-S261 × 10 (2.61 MWh) EQS-2000R
1250 kW backup power (10 units) Dual-mode operation (full-power charging) D-Cube-S261 × 10 (2.61 MWh) EQS-4000R ⚠️⚠️
1250 kW backup power (10 units) Dual-mode operation (charging limited ≤ 80 kW/unit) D-Cube-S261 × 10 (2.61 MWh) EQS-2600R ⚠️
1250 kW backup power (10 units) Dual-mode operation (off-peak) D-Cube-A500 × 2 + D-Cube-261D × 8 (2.088 MWh) EQS-2000R
1250 kW backup power (10 units) Dual-mode operation (off-peak) D-Cube-A500 × 3 + D-Cube-261D × 12 (3.132 MWh) EQS-2000R

2.8 Summary of Core Selection Formulas

EQS Apparent Capacity (kVA) ≥ [PCS Charging Power (kW) + Load Power (kW)] / cosφ

S_EQS ≥ (N × P_charge + P_load) / cosφ

Where:
  S_EQS    EQS apparent capacity (kVA)
  N        Number of PCS units
  P_charge Single PCS charging power (kW); equals 0 in single-condition operation
  P_load   Load power (kW)
  cosφ     Power factor (typically 0.90-0.98 after commercial/industrial compensation)

Red Line R6 (Selection Determined by Dual-Condition Operation):

Operating Condition Total Power for Dual Conditions Recommended EQS Selection
Single condition (load only, battery not charging) P_load / cosφ Table in §6.2
Dual condition (charging + load simultaneously, the most stringent) (N × P_charge + P_load) / cosφ Table in §6.3 / Case in §6.9

Red Line R7:

10 PCS units charging at full power + 1250 kW full load simultaneously → total power 2500 kW → EQS-4000R (2770 kVA) must be selected, and cosφ ≥ 0.91.

3 Product Portfolio Topology Diagram

3.1 EQS Electrical Wiring Diagram

ScreenShot_2026-09-16_140748_975
ScreenShot_2026-09-16_140803_574

3.2 S-Series Integrated Energy Storage Cabinet (PCS + Battery Integrated)

Model PCS Power Energy Storage Capacity Battery Type Cooling Communication
D-Cube-S125/261-EU (VG) 125 kW (VSG version) 261 kWh LFP 314Ah Liquid cooling Modbus TCP / CAN with VG sampling
6544122_01
Single D-Cube-S125/261-EU + EQS-500(4)R
6544122_02
Multiple D-Cube-S125/261-EU + EQS
  • The detailed configuration table is as follows:
Energy Storage Product Model Quantity Power Capacity Recommended EQS Model EQS Rated Current QS Rated Power Working Mode
D-Cube-S125/261-EU (VG) 1 125kW 261kWh EQS-500(4)R 500A 346 kVA @400V Dual-mode
D-Cube-S125/261-EU (VG) 2 250kW 522kWh EQS-750(4)R 750A 520 kVA @400V Dual-mode
D-Cube-S125/261-EU (VG) 3 375kW 783kWh EQS-1300(4)R 1300A 1385 kVA @400V Dual-mode

3.3 A-Series PCS Integrated Cabinet + 261D Battery Cabinet

The A-Series is an outdoor PCS integrated cabinet launched by HOENERGY, designed to work in conjunction with the D-Cube-261D battery cabinet (physically separate from A, connected via DC bus). The A-Series PCS is also based on the Eneri 125 kW module (sharing the same PCS hardware platform as the S-Series), with verified compatibility against Eneri EQS switching.

6544122_03
PCS Integrated Cabinet Model PCS Power Matching 2h 4h 6h 8h Backup
D-Cube-A250 250 kW (= 2×125 kW modules) 2×261D 4×261D 6×261D 8×261D
D-Cube-A375 375 kW (= 3×125 kW modules) 3×261D 6×261D 9×261D 12×261D
D-Cube-A500 500 kW (= 4×125 kW modules) 4×261D 8×261D 12×261D 16×261D
Battery Cabinet Model Storage Capacity Battery Type Cooling Dimensions
D-Cube-261D 261 kWh LFP 314Ah Liquid Cooling 1300×1200×2280 mm

A-Series vs S-Series Selection Comparison:

Dimension S-Series Integrated Cabinet A-Series PCS + D Battery Cabinet
Integration PCS + battery in one cabinet PCS cabinet + battery cabinet (2 separate units)
Power per Cabinet 125 kW 250/375/500 kW
Storage per Cabinet 125/261 kWh 2-16×261 kWh via 261D stacking
Footprint Compact A cabinet + N×D cabinets, flexible
Maintenance Single-cabinet maintenance Independent PCS/battery maintenance
Applicable Scenarios Small-to-medium C&I (≤1 MW) Medium-to-large C&I (1-5 MW)
EQS Compatibility ✅ Verified ✅ Verified (same Eneri 125 kW PCS module)
Applicable EQS EQS-500/750/1300/2000R EQS-1300/2000/2600/4000R (high-current scenarios)

A-Series Integration Example (2 MWh typical configuration):

  • D-Cube-A500 (500 kW PCS) × 2 + D-Cube-261D × 8 = 1000 kW PCS + 2.088 MWh
  • Connect to EQS-2000R (13385 kVA) or EQS-4000R (2770 kVA)
  • For detailed A-Series solutions, please contact HOENERGY technical staff

D-Cube to EQS Interface:

D-Cube AC Output (U/V/W/N2)  ──►  EQS Load-side Terminal
D-Cube DI/DO (VSG Switching) ──►  EQS Control Terminal DO4+/DO4-, DI3+/DI3-
D-Cube VSG Algorithm Enable  ──►  0x5066 / 0x02FF Pre-configured

§4 EQS Internal Structure + ≤20 ms Switching Principle

4.1 EQS Static Switch Core Components

The core of the EQS is a bidirectional thyristor (SCR) anti-parallel static switch, where each pole (A/B/C or plus N) consists of two SCRs connected in anti-parallel to form a bidirectional conduction unit. This is the fundamental reason it can achieve a switching time of ≤20 ms.

Component Quantity Function
Thyristor (SCR) 2 per pole, anti-parallel Main power path, zero-cross natural commutation
Bypass Contactor 1 per pole Steady-state conduction, reduces SCR conduction losses
Gate Driver 1 per pole Sends SCR gate trigger pulses
Current Transformer (CT) 3 Detects main circuit current, zero-cross detection
Voltage Transformer (VT) 3 Detects grid-side/PCS-side voltage, synchronization detection
Controller 1 DO4/DI3 communication, state machine, fault protection
Auxiliary Contacts (NO/NOC/NC/NCC) 4 channels Status feedback to SCADA

4.2 Key Question: Is EQS Pure Solid-State or a Solid-State + Mechanical Hybrid?

Q. Is the EQS a pure solid-state switch (SCR only) or a solid-state + mechanical hybrid?

🔴 A. Solid-state + mechanical hybrid (Hybrid Static Switch) — this is the key design that enables the EQS's 99.97% full-load efficiency:

Mode Path Time Window
Steady State Mechanical bypass contactor conducts (no SCR conduction voltage drop) Continuous operation
Switching transient (≤20 ms) SCR turns on + mechanical bypass opens <20 ms
Switching complete Mechanical bypass conducts again + SCR turns off After switching

4.3 ≤20 ms Switching Sequence

Grid-tied → Off-grid (Grid Power Loss):

t=0 ms      Grid fault
t<5 ms      PCS detects bypass voltage 0x0AAF: 0→2 (transient)
t=5-10 ms   EQS control board judges: grid power loss → triggers SCR pre-turn-on preparation
t=10-15 ms  EQS mechanical bypass opens (contact separation)
            + SCR takes over conduction (natural commutation, switched at current zero-crossing)
t=15-20 ms  Mechanical bypass fully open, load current entirely flows through SCR
            + PCS switches to off-grid VSG mode (0x5066=1, 0x02FF=1)
t≤20 ms     Switching complete, load continuously powered by PCS VSG
            + 0x0219 STS control command: 1→0
            + 0x0F3A A3 board DI3 feedback external switch opened

Off-grid → Grid-tied (Grid Recovery):

t=0 s       Grid recovery (0x0AAF: 1→2→0)
t=0 s       PCS enters auxiliary secondary frequency regulation phase
            - EMS reads 0x018C/0x018D to calculate P_tot/Q_tot
            - Sets P_tot/n down to 0x500E (Pset), step ≤10%, interval ≥100 ms
t=90-180 s  Frequency/voltage aligned with grid reference
t=closing instant  EQS mechanical bypass closes (at current zero-crossing)
            + 0x0219 STS control command: 0→1
            + 0x0F3A DI3 feedback external switch closed
t=after closing    SCR naturally turns off, steady-state path resumes mechanical bypass conduction
            + PCS switches to grid-tied VSG mode (0x5066=0)

4.4 Zero-Current Switching Principle

The key for EQS to achieve ≤20 ms is Natural Commutation:

Q. What is natural commutation? Why must switching occur at zero current?

🔴 A. Natural commutation = leveraging the characteristic that the AC current itself crosses zero every 10 ms (50 Hz), completing the SCR channel switching at the instant of current zero-crossing.

  • SCR is a semi-controlled device; once it is turned on, it must wait for the current to cross zero before it can be turned off (it cannot be forcibly turned off);
  • At 50 Hz mains frequency, the current crosses zero once every 10 ms, so a zero-crossing point is guaranteed within at most 10 ms;
  • EQS switches at the current zero-crossing point → zero-current switching, with no arc, no inrush, and no voltage spike;
  • This is why the EQS can achieve a lifetime of 1,000,000 cycles (pure mechanical switches suffer contact erosion from arcing, while pure solid-state SCRs incur large continuous conduction losses).
eqs_natural_commutation_v1_en

§5 EQS Lifetime Curve + Reliability Data

5.1 EQS Lifetime Algorithm (Hard Selection Criterion for Projects)

EQS Lifetime Selection Formula:

EQS Design Lifetime ≥ Project Lifetime × Annual Switching Cycles × Safety Factor

Where:
- Project Lifetime = 15 years (industrial and commercial standard)
- Annual Switching Cycles = Number of grid anomalies/year × Safety Margin (2-3x)
- Safety Factor = 1.5 (conservative)

Typical Project Lifetime Calculation Examples:

Project Type Estimated Switching Cycles/Year 15-Year Total Switching Cycles Recommended EQS Lifetime Corresponding Model
Stable Grid (Mainstream) 5-10 cycles 75-150 cycles 100,000 cycles EQS-500/750/1300 Standard Model
Weak Grid (Diesel-Storage Hybrid) 50-100 cycles 750-1500 cycles 100,000 cycles Same as above
Frequent Switching (Dense Backup Power) 200-500 cycles 3000-7500 cycles 100,000 cycles Same as above
Extremely Frequent (Data Center N+1 Drill) 1000-2000 cycles 15000-30000 cycles 1,000,000 cycles EQS-100W Long-Life Model

5.2 Source of the 1,000,000-cycle lifespan (ENJOY in-house test)

The EQS 1,000,000-cycle lifespan comes from in-house testing at the ENJOY factory. Key data:

Test Item Test Condition Measured Result Standard
Mechanical life Rated current 1300 A, cosφ=0.8, switching frequency 60 ops/h ≥1,000,000 cycles (no failure) GB 14048.11 / IEC 60947-6-1
Electrical life Rated current 1300 A, AC-33 category (motor load) ≥100,000 cycles (contact wear < 0.5 mm) IEC 60947-4-1
Short-time withstand 20 kA / 1 s Passed IEC 60947-1
Temperature rise Rated current 1300 A continuous operation Terminal temperature rise < 65 K IEC 60947-1
Dielectric strength 2500 VAC / 1 min Passed IEC 60947-1
EMC ESD / electrical fast transient / surge Class B (industrial grade) IEC 61000-4

Key interpretation: 1,000,000 cycles refers to the mechanical life (excluding contact wear); the electrical life (including contact wear) is ≥100,000 cycles.
The EQS standard model is factory-rated at 100,000 cycles, while the long-life model is rated at 1,000,000 cycles.

5.4 Selection Recommendations (by Project Type)

Project Type Recommended Cycle Life Selection Suggestion Remarks
Commercial & Industrial Backup Power 100,000 cycles EQS Standard Type Fewer than 1,000 switchovers within a 15-year lifespan; the standard type is sufficient
Weak Grid (Diesel-Storage Hybrid) 100,000 cycles EQS Standard Type Same as above
Data Center Periodic Drills 1,000,000 cycles EQS Long-Life Type Drill switchovers are intensive; redundancy is required
Semiconductor Plant (Sensitive Loads) 1,000,000 cycles EQS Long-Life Type Unplanned downtime is unacceptable

§6 Three Core VSG Mechanisms + Coordination with EQS

6.1 Three Core Mechanisms of VSG

Mechanism Simulated Object Function Key Parameters (PCS Built-in)
Virtual Inertia J Rotor Kinetic Energy Suppresses RoCoF (Rate of Change of Frequency), preventing instantaneous collapse InertiaTC = 0x02F8 (1-15, default 1)
Virtual Damping D Damping Winding/Friction Negative feedback suppresses transient oscillations fKDamp = 0x02FC (300-500, default 500)
Primary Frequency Regulation Kf Governor Characteristic P-f droop control, steady-state recovery nKfCoefByPload = 0x02FA (10-100, default 70)

6.2 EQS Switching and VSG Three-Mechanism Coordination Timing

                 EQS Mechanical Action        VSG Algorithm Response
                 ─────────────                ────────────
t=0 ms           Grid fault                    PCS detects 0x0AAF=2 (transient)
                                                  ↓
t=0-5 ms         EQS triggers SCR preparation PCS J (virtual inertia) starts
                                                  Releases "virtual rotor kinetic energy"
                                                  Suppresses frequency drop RoCoF
                                                  ↓
t=5-15 ms        EQS mechanical bypass opens   PCS D (virtual damping) starts
                 SCR takes over conduction      Negative feedback suppresses transient oscillation
                                                  ↓
t=15-20 ms      EQS fully opens               PCS Kf (primary frequency regulation) starts
                 Load 100% via SCR              P-f droop, steady-state recovery
                                                  ↓
t≤20 ms          Switching complete            PCS already in steady-state operation
                                                  0x5066=1, 0x02FF=1
                                                  0x500E Pset dispatch command
                                                  ↓
t>20 ms          Steady-state mechanical bypass open VSG continues grid-forming
                 SCR off                        Waits for 0x0AAF=0 (grid recovery)

6.3 Grid-Side Fault — 1.5× Rated Power / 200 ms Grid-Forming Support

Q. Why can the VSG provide 1.5× rated power for 200 ms?

🔴 A. Two layers of reasons:

Layer Reason
Hardware Layer Hoenergy PCS hardware overload capability of 150% (200 ms), with IGBT module selection redundancy
Algorithm Layer The three VSG mechanisms (J+D) collaborate to release "virtual rotor kinetic energy" at the instant of a fault, emulating the fault current characteristics of a synchronous generator

Application Value:

  • In mainstream 0.4 kV commercial and industrial scenarios, instantaneous grid faults (lightning strikes, equipment short circuits) occur approximately 5-10 times per year;
  • The VSG's 1.5× support capability enables the PCS to actively inject reactive power during faults, supporting grid-side voltage recovery;
  • This is something a pure PQ-controlled PCS cannot achieve — PQ mode merely follows commands and does not actively support the grid.

7 Detailed Benchmark Case Study: Dual-Condition Selection for 10 PCS Units

Q. Customer Question: I need 10 PCS units of 125 kW each (10 × 125 = 1250 kW total PCS power). The load is also 1250 kW (full load), and charging and the load occur simultaneously. Which EQS should I select?

7.1 Charging + Load Power Stacking

Known:

  • Number of PCS units N = 10
  • Total PCS power = 10 × 125 = 1250 kW
  • Total load power = 1250 kW (full load, no margin)
  • Charging and load occur simultaneously (time-of-use tariff-free scenario or customer requires 0 switching)
  • Total charging power = 10 × 125 = 1250 kW

Calculation (Red Line R6):

Item Value
Total PCS charging power 10 × 125 = 1250 kW
Total load power 1250 kW (full load)
Total power under dual operating conditions 1250 + 1250 = 2500 kW
Apparent power (cosφ 0.8) 2500 / 0.8 = 3125 kVA ️
Apparent power (cosφ 0.85) 2500 / 0.85 = 2941 kVA ️
Apparent power (cosφ 0.9) 2500 / 0.9 = 2778 kVA ️ Critical
Apparent power (cosφ 0.91) 2500 / 0.91 = 2747 kVA ️ EQS-4000R boundary
Apparent power (cosφ 0.95) 2500 / 0.95 = 2632 kVA ✅ EQS-4000R with margin
Apparent power (cosφ 1.0) 2500 / 1.0 = 2500 kVA ✅

7.2 Candidate EQS Model Comparison (10 PCS Units at Dual-Mode Full Power)

EQS Model 400 V Capacity (kVA) cosφ 0.8 Margin cosφ 0.9 Margin cosφ 0.95 Margin Selection Conclusion
EQS-2000R (3P) 1385 -56% overload ❌ -50% ❌ -47% ❌ Far from sufficient
EQS-2600R (3P) 1800 -42% overload ❌ -35% ❌ -32% ❌ Far from sufficient
EQS-4000R (3P) 2770 -11% overload ❌ +0.3% critical ⚠️ +5% ✅ Must select cosφ ≥ 0.91 ⚠️⚠️⚠️

Key Conclusion (Red Line R7): 10 PCS units at full-power charging + 1250 kW full load simultaneously → EQS-4000R (2770 kVA) is the only viable model, but with hard engineering constraints:

  • cosφ < 0.91 → EQS-4000R overloads (red line triggered; must derate or upsize)
  • cosφ ≥ 0.91 → EQS-4000R safe (typically achievable at 0.92-0.98 after industrial SVG/capacitor compensation)
  • cosφ ≥ 0.95 → EQS-4000R with 5% margin (ideal operating condition)

7.3 Four Engineering Compromise Path Options (Sorted by Priority)

Path Description Dual-Mode Actual Power Recommended EQS Engineering Feasibility
Path 1: Off-Peak Charging (Most economical) EMS schedules the charging window to avoid load peaks (e.g., 23:00–07:00) Actual single-mode 1250 kW (cosφ 0.8 = 1563 kVA, cosφ 0.95 = 1316 kVA) EQS-2000R (cosφ ≥ 0.9 safe / cosφ 0.95 with 5% margin) ✅ Mainstream solution in the Czech market, aligned with time-of-use tariffs
Path 2: Limit Charging ≤ 50 kW/unit + EQS-4000R (Dual-mode available) EMS limits charging to 50 kW/unit (battery starts charge limiting from 80% SoC) 10×50 + 1250 = 1750 kW (cosφ 0.8 = 2188 kVA / cosφ 0.9 = 1944 kVA / cosφ 1.0 = 1750 kVA) EQS-4000R (2770 kVA with 26%–58% margin) ✅ Charging time extended 2.5×, but large EQS safety margin
Path 3: Limit Charging ≤ 30 kW/unit + EQS-2600R (Extreme limitation) EMS limits charging to 30 kW/unit (battery starts charge limiting from 70% SoC) 10×30 + 1250 = 1550 kW (cosφ 0.9 = 1722 kVA / cosφ 0.95 = 1632 kVA) EQS-2600R (1800 kVA with 4%–10% margin) ⚠️ Charging time extended 4.2×, engineering edge case
Path 4: Direct EQS-4000R (No compromise) Full-power charging + load without power limiting 2500 kW = 2778 kVA (cosφ 0.9 critical) EQS-4000R (requires cosφ ≥ 0.91) ⚠️⚠️ Requires SVG/capacitor compensation cabinet, strictly engineered

Recommended Solutions:

Customer Type Recommended Path EQS Selection Engineering Coordination
Time-of-use tariff users Path 1: Off-Peak Charging EQS-2000R EMS scheduling strategy
Industrial & commercial backup (charging + load must run simultaneously) Path 2: Limit Charging 50 kW + EQS-4000R EQS-4000R EMS power-limiting strategy + extended charging time
Large data center backup (millisecond-level response) Path 4: Direct EQS-4000R + SVG Compensation EQS-4000R SVG/capacitor cabinet to keep cosφ ≥ 0.91
Compact footprint projects Path 3 + A-Series Cabinet EQS-2600R A500 × 3 + 261D × 12

§8 EQS Wiring and Signal Definition

7.1 Power Terminals

Terminal Type Silkscreen Function Remarks
Grid Side R Grid input L1 phase
S Grid input L2 phase
T Grid input L3 phase
N1 Grid input N line EQS-2000R is 3P without N1 (red cable R2)
Load Side U Connects to PCS AC output L1 phase
V Connects to PCS AC output L2 phase
W Connects to PCS AC output L4 phase
N2 Connects to PCS AC output N line

Note: In the source table, the third load-side phase is labeled "W" with the description "连接 PCS 交流输出 L4 相" (L4 phase). The discrepancy between W and L4 is preserved as in the original.


Translation Notes: - 功率端子 → Power Terminals - 端子类型 → Terminal Type - 丝印 → Silkscreen - 功能 → Function - 备注 → Remarks - 电网侧 → Grid Side - 负载侧 → Load Side - 电网输入 L1 相 → Grid input L1 phase (L1, L2, L3 preserved as technical labels) - 电网输入 N 线 → Grid input N line - EQS-2000R 为 3P 无 N1 → EQS-2000R is 3P without N1 - 红线 R2 → red cable R2 - 连接 PCS 交流输出 L1 相 → Connects to PCS AC output L1 phase - 连接 PCS 交流输出 N 线 → Connects to PCS AC output N line

All Chinese characters have been translated to English. Technical identifiers (EQS-2000R, PCS, R, S, T, U, V, W, N1, N2, L1, L2, L4, R2, 3P) are preserved in their original Latin/numeric form.

7.2 Control Terminals (Core: DIO Digital I/O)

Terminal Silkscreen Function Signal Direction
24V 24V External 24 V auxiliary power positive External power supply
GND GND External 24 V auxiliary power ground External power supply
DO4+ DO4+ Digital input, receives the switching permission command issued by the PCS PCS → EQS
DO4- DO4- (Signal routed to the PCS side) PCS → EQS
DI3+ DI3+ Dry contact output, feeds back the EQS status to the PCS EQS → PCS
DI3- DI3- (Signal routed to the PCS side) EQS → PCS
NO NO Auxiliary feedback contact 1 – Normally Open EQS status
NOC NOC Auxiliary feedback contact 1 – Common EQS status
NC NC Auxiliary feedback contact 2 – Normally Closed EQS status
NCC NCC Auxiliary feedback contact 2 – Common EQS status

7.3 Control Power Input

Terminal Function
L 220 VAC power input (phase/line)
N 220 VAC power input (neutral)
PE Protective earth

⚠️ Red Line R9: The EQS control power 220 VAC must be supplied independently and must not be drawn from the PCS DC bus (to avoid power loss during switching transients).

7.4 EQS-D-Cube Signal Flow Diagram

ScreenShot_2026-09-16_140748_975
Figure: EQS + D-Cube PCS Signal Flow and Power Flow

7.5 Factory Pre-Integration Interfaces (D-Cube ↔ EQS)

Interface Factory Pre-Fabricated On-Site Installation
Power lines (U/V/W/N2) — D-Cube AC output → EQS load side
DO4/DI3 control lines — D-Cube DI/DO terminals → EQS DO4/DI3
CAN communication line (if required) Weak inter-PCS communication: transmit off-grid signal —
Control power 220 VAC — Independent loop (do not draw power from PCS)
Grid side R/S/T/N1 — Customer connects to grid
Load side (EQS output) — Customer connects load

§8 Four Working Modes

8.1 Mode Overview

Mode Trigger Condition EQS Position PCS Mode
M1 Grid-Connected Grid normal Closed (grid side energized) Grid-Connected PQ (default)
M2 Switching (Grid-to-Island) 0x0AAF: 0→2 ≤20 ms open Automatic switch to Island VSG
M3 Islanded Grid power loss Open Island VSG grid-forming
M4 Switching (Island-to-Grid) 0x0AAF: 1→2→0 90-180 s close Secondary frequency regulation assist → close → Grid-Connected PQ

§9 FAQ 与待澄清问题

9.1 FAQ (sorted by inquiry frequency)

Q1. Is the switchover time ≤20 ms real?

🔴 A. EQS "paired with a 125 kW (IP20) PCS ≤20 ms" requires the PCS to be in VSG mode and the DO4/DI3 wiring to be correct.

Q2. After switching to off-grid, how long can the PCS keep running?

🔴 A. Determined by the energy storage capacity. A D-Cube-S125 (125 kWh) running at full load of 125 kW can sustain for 1 hour; a D-Cube-S261 (261 kWh) can sustain for 2 hours at full load; the A series can last up to 8 hours. When SOC falls below 20%, it is recommended to switch to diesel generator or reduce the load.

Q3. Why is the VSG paralleling upper limit 10 units instead of 12?

🔴 A. The VSG algorithm itself supports 12 units, but it is currently limited to 10 units for three reasons:

  1. SOC balancing stability: 10 units is the upper limit based on engineering experience;
  2. EQS single-unit current density: 10 units × 125 kW = 1.25 MW, which keeps the current density of the EQS-2000R (2000 A) manageable;
  3. Future expansion: Phase II of the project can be expanded to 12 units (the theoretical VSG upper limit) without replacing the EQS.

Q4. How is SOC consistency ensured when multiple PCS units are paralleled?

🔴 A. The EMS issues secondary frequency regulation commands via 0x500E/0x500F to allocate power proportionally to SOC. Hard constraint: the power spread among PCS units must be ≤ (total load / number of PCS units) × 20%.

Q5. The EQS-2000R is 3P without N1. Can it be used in TN-C/TN-S systems?

🔴 A. This needs special confirmation. The 3P model has no N1 terminal. If the load in a TN-C/TN-S system requires an N line, a 4P model (EQS-500/750/1300) must be selected, or an external neutral-point treatment must be used.


Appendix A Key Red Lines

A.1 Design Red Lines (Violation will render the solution invalid)

Red Line Numbering Convention: R1-R5 = General engineering constraints (§0.2 cheat sheet); R6-R10 = This project's §6 selection hard constraints (directly drive the §6.x tables); R11-R12 = VSG parameter boundaries (verified during commissioning).

# Red Line
R1 EQS switching time ≤20 ms only holds when paired with the 125 kW IP20 PCS; for the 215 kW IP66 PCS the value is ≤30 ms
R2 EQS-2000R is a 3P device without an N1 terminal; TN-C/TN-S systems must select the 4P model or use an external neutral-point treatment
R3 The current upper limit for VSG paralleling is 10 units;
R4 Off-grid SOC balancing hard constraint: the power spread between any two PCSs must be ≤ (total load / number of PCSs) × 20%
R5 Secondary frequency regulation step ≤10% of rated power, interval ≥100 ms; synchronized closing duration 90-180 s
R6 EQS capacity must be ≥ PCS charging power + load consumption power (must be satisfied under any operating condition; see formula in §6.8)
R7 10 PCSs at full power under dual operating conditions → must select EQS-4000R (2770 kVA), with cosφ ≥ 0.91
R8 The EQS control power supply (220 VAC) must be independently powered and must not be drawn from the PCS DC bus