Skip to content

What Are the Operating Modes of a PCS?

In-Depth Technical Analysis of the Four Major PCS Control Modes

PQ · VF · VSG · Grid-Following (GFL) · Grid-Forming (GFM)


1 Panoramic Quick View

01_four_modes_overview_en

1.1 Core Comparison

Mode Role Control Objective Follows Whom Grid Dependency
PQ Grid-Following Worker Output P/Q Grid Very strong
VF Islanded Boss Output U/f Internal reference None
VSG Grid-Forming Steady Boss Output U/f + inertia Self inertia None
GFM (general term) Active support VF + VSG + droop Self Weak
GFL (general term) Passive follower PQ + PLL Grid Strong

Mnemonic: Grid-following relies on phase-locking, grid-forming relies on virtual synthesis; when the grid is strong use grid-following, when the grid is weak use grid-forming.


2 Why Does a PCS Need "Multiple Identities"?

The awkward position of an energy-storage PCS: to whom does the "controllable" output ultimately listen?

  • Listen to the grid → Worker (PQ)
  • Listen to itself → Boss (VF)
  • Dress up as the fighter-jet version of the Boss → VSG
Choice Physical Essence Analogy
Grid-Following PQ Current source (high internal impedance) Worker
Grid-Forming VF Voltage source (low internal impedance) Boss
Grid-Forming VSG Voltage source + flywheel Steady Boss

2 PQ Mode (Worker)

"Boss (the grid) tells me how much power, I output exactly that much power"

2.1 Control Architecture

02_pq_control_architecture_en PQ mode adopts the classic "dual-loop + PLL" structure: outer power loop + inner current loop + phase-locked loop. The PLL is the key; without it the mode cannot operate.

2.2 PLL's Fatal Weakness

Grid Condition PLL Behavior PCS Impact
Ideal grid ✅ Locks quickly Normal operation
Harmonic distortion ⚠️ Jitters Power oscillation
Weak grid, SCR < 2 ❌ Loses lock Mode fails
Complete grid outage ❌ No signal PCS shuts down

2.3 Applicable Scenarios

✅ Grid connection to a strong grid (SCR > 3), AGC/AVC dispatch response, peak shaving and valley filling ❌ Not suitable for weak grids or black-start


3 VF Mode (Boss)

"Grid is gone? No problem, I'll be the boss!"

3.1 Control Architecture

VF mode has no PLL; it directly uses an internal reference (U = 400 V, f = 50 Hz) as the voltage source. Voltage outer loop + current inner loop achieves constant voltage and constant frequency.

3.2 Multi-Unit Paralleling: Droop Control

Multiple PCSs require only communication to automatically share power. Principle: when output is higher, frequency/voltage droops slightly → automatic balance.

Tuning Principle: droop coefficient × rated capacity of every PCS must be equal → only then is power sharing achieved.

3.3 Hard Constraints of VF

  • Load < PCS capacity (otherwise voltage collapses)
  • Short-circuit current only 1.2–1.5× (no inertia)
  • Fixed frequency (no governor)
  • Poor resilience to impact loads (undamped second-order system)

3.4 Applicable Scenarios

✅ Microgrid islanded operation, black-start, UPS mode, master-slave switching of multiple PCSs ❌ Not suitable for scenarios requiring inertia support


4 VSG — Virtual Synchronous Generator (the Steady Boss)

"I pretend to be a real synchronous generator, with inertia!"

4.1 Core Idea

03_vsg_model_en

Inside the VSG there is a virtual flywheel that emulates the rotor motion of a synchronous generator, making the PCS behave like a real generator.

Real Synchronous Machine VSG Algorithm
Physical flywheel Software parameter J (pu·s²)
Physical damper Software parameter D (pu·s/rad)
Synchronous reactance Virtual reactance X_s (pu)
Excitation system Software excitation regulator
Governor Software droop

4.2 Complete Mathematical Model

(1) Rotor motion equation (core): J × angular acceleration = mechanical torque − electromagnetic torque − damping × frequency deviation

(2) Virtual impedance: EMF = terminal voltage + virtual impedance × current

(3) Excitation regulation: EMF = initial value + reactive-droop coefficient × (Q_ref − Q)

(4) Governor: mechanical torque = initial value + active-droop coefficient × (P_ref − P)

4.3 Influence of J / D / X_s Parameters

Parameter Large Small
J (inertia) Strong disturbance rejection / slow response Fast response / prone to instability
D (damping) Small steady-state deviation / large power oscillation Smooth power / large frequency deviation
X_s (reactance) Good power decoupling / large voltage drop Strong voltage support / power coupling

4.4 Frequency-Response Comparison

  • 🔴 VF: on a sudden load change it drops instantly to 49.5 Hz, may trip
  • 🟢 VSG: drops gradually to 49.8 Hz over 0.5 s, then recovers smoothly

The VSG's "dip slowly and recover" buys time for grid equipment to react — this is the value of inertia.

4.5 Golden Rules of Tuning

  1. J must not exceed the system's equivalent inertia — otherwise frequency response is too slow
  2. D must be greater than J × angular speed — otherwise underdamped oscillation ⚠️
  3. X_s must match the grid impedance — otherwise power coupling
  4. J/D of all GFM units must be coordinated — otherwise power circulating currents between parallel units
  5. Frequency-droop coefficient must be uniform across the whole grid — otherwise power-grabbing

4.6 Applicable Scenarios

✅ Connection to weak grids (SCR < 2), high-renewable-penetration areas, black-start, islanded microgrids, frequency and peak regulation


5 Grid-Forming vs. Grid-Following

5.1 System Evolution Trend

In the renewable era, grid-following converters are proliferating, and the grid is becoming increasingly fragile. Grid-forming energy storage is the solution.

5.2 Core Comparison

Dimension 🔴 Grid-Following (GFL) 🟢 Grid-Forming (GFM)
Physical model Current source Voltage source
PLL dependency Required Not required
Short-circuit current < 1.2× 1.5–3×
Frequency response Only power regulation Directly influences frequency
Inertia support ❌ None ✅ Yes
Black-start ❌ Cannot ✅ Can
SCR requirement SCR ≥ 2–3 Works with SCR < 1

5.3 Grid Strength (SCR) vs. Control Mode

SCR Recommended Mode Cost
> 5, very strong PQ is fully OK ⭐
3–5, strong PQ is usable ⭐⭐
2–3, medium PQ carries risk, GFM recommended ⭐⭐⭐
< 2, weak GFM mandatory, VSG provides strong support ⭐⭐⭐⭐
< 1.5, very weak VSG mandatory ⭐⭐⭐⭐⭐

6 Terminology Quick-Reference Table

Abbreviation Full Name Meaning in One Line
PLL Phase Locked Loop The "ear" that listens to the grid's rhythm
SCR Short Circuit Ratio How strong the grid is
d/q axis d/q axis The two DC components after decomposing three-phase AC
J Virtual Inertia The flywheel weight of the VSG
D Damping The shock absorber of the VSG
X_s Virtual Reactance The virtual internal resistance of the VSG
SVPWM Space Vector PWM The switching algorithm that converts DC to AC
SoC State of Charge The battery's fuel gauge
EMS Energy Management System The brain of the energy-storage system
STS Static Transfer Switch The fast on-grid/off-grid gate
GFM Grid-Forming Be the grid yourself
GFL Grid-Following Follow the grid
VSG Virtual Synchronous Generator Pretend to be a synchronous generator
LVRT Low Voltage Ride-Through Withstand voltage dips without disconnecting
PQ Power Control Controls only active/reactive power
VF Voltage/Frequency Control Controls voltage and frequency