Energy Storage Converter (PCS) Off-Grid Mode — Application Guidelines for Different Load Characteristics

1. Pure Resistive Loads

  • Load power ≤ PCS rated power;100% load-carrying capability is supported.
  • Recommended sizing ratio: 80% of rated load capacity.

2. Pure Inductive Loads

  • Load power ≤ 15%–20% of PCS rated power.
  • Examples of such loads: direct-on-line motors, water pumps, electric drills, air conditioners (non-inverter type), and other inrush loads.

3. Inverter-Type Loads

  • Load power ≤ 60% of PCS rated power.
  • For conventional loads such as inverter air conditioners + lighting, the loading ratio shall be configured at ≤ 70% of PCS rated power.

4. Special Loads

  • Applicable objects: loads with high power-quality requirements, such as tungsten stage lights and AC EV charging stations.
  • Treatment method: add an isolation transformer at the AC output of the PCS.
  • Recommended transformer type: Dyn11.
  • Purpose: to enhance reliability and anti-interference capability.

5. PCS Off-Grid Mode Operating Parameters

  • Power factor ≥ 0.8 (for pure resistive loads).
  • Single module: the single-step loading ratio can support 100% connection/disconnection; 80% connection is recommended.
  • Multi-module off-grid start-up: the single-step loading ratio is recommended at ≤ 40%, with the remaining load connected gradually.
  • Special applications: the design scheme and load characteristics must be confirmed in detail with Enjie (恩玖) technical personnel to determine the appropriate PCS capacity sizing.

6. Single-Phase Output

  • Single-phase output is also subject to the limitations stated above.
  • 100% unbalanced load carrying is supported.
  • Single-phase rated power equals 1/3 of the PCS rated power.