Skip to content

Off-Grid Startup Guide

D-Cube-H125 / H261 + Solis 125K — Off-Grid / Backup / Generator / Paralleling

Document version: V1.0 (2026-08-26) Scope: BESS selection / bidding / engineering implementation for EU off-grid + backup + generator scenarios Hybrid inverter: Solis S6-EH3P125K10-NV-YD-H (125 kW)

1. Three Off-Grid Application Modes

Mode Trigger Condition Primary Source Backup Source
Backup (grid-storage mutual backup) Grid outage Battery → PV → Generator —
Off-grid (fully islanded) No grid PV + Battery + Generator All
Hybrid grid-tied (normal) Grid normal PV → Battery / Load / Grid Battery + Generator

2. Backup Output — 125 kW Continuous + < 10 ms Transfer

2.1 Key Facts

  • 125 kW is continuous rated, not peak
  • < 10 ms transfer certified by G99 Type B test (TÜV SÜD report 704092514279-00)

2.2 125K Backup Parameters

Parameter Value
Backup rated output power 125 kW
Backup rated output current (380 V) 189.9 A
Backup rated output current (400 V) 180.4 A
Rated output voltage 3/N/PE, 230 V / 400 V
THDv (under linear load) < 2 %
Backup transfer time < 10 ms
Maximum phase imbalance 100 %
Maximum single-phase power 41.66 kW
Peak overload (top envelope) 1.2× 100 s / 1.4× 10 s / 1.6× 200 ms
Frequency 50 Hz / 60 Hz selectable

2.3 Transfer Time Details

  • Grid-tied → Off-grid (grid loss): < 10 ms (automatic)
  • Off-grid → Grid-tied (grid restoration): Wait for V/f stabilization, then synchronize (tens of seconds, depending on grid stability)
  • PV → Battery: Internal DC-bus transfer, no interruption
  • Generator → Battery: Controlled by SOC threshold, see §7

3. Overload Curve

3.1 125K Overload Capability

Overload Level 125K Derating Factor
1.2 × (= 150 kW) 100 s 6× shorter
1.4 × (= 175 kW) 10 s 10× shorter
1.6 × (= 200 kW) 200 ms 50× shorter

3.2 Design Consequences

  • ❌ Customer starts 200 kW motor load, single 125K will trip (even at 10 s)
  • ❌ Alarm Over-Load or OV-ILLC (user manual p.78, 81)
  • ✅ 125K starting 200 kW locked-rotor load → must split into 2 units

3.3 Design Margin for Key Application Scenarios

Load Type Startup Surge 125K Design Margin
Resistive (electric heating, incandescent) 1.0 × ✅ Sufficient
Motor soft-start (VFD) 1.2–1.4 × / 5–10 s ✅ OK
Motor direct-on-line (DOL) 5–7 × locked-rotor ❌ Must use VFD or split units
Large transformer inrush 8–12 × / 100–200 ms ⚠️ 125K's 1.6×/200 ms may not suffice, on-site test required
UPS / PSU capacitor charging 2–3 × / 50–200 ms ❌ Not supported (> 1.6×)
Welding equipment 2–5 × ❌ Not supported
Heat pump (compressor startup) 3–5 × / 200 ms ⚠️ Use with caution, phased startup required

4. Black-Start Matrix

4.1 Comparison of 5 Startup Sources

Startup Source Black-start Supported Condition
PV + Battery ✅ Recommended Standard self-consumption sequence
Battery only (no PV) ✅ SOC ≥ 5–10 % (defined by battery vendor)
PV only (no battery) ✅ Enable PV-only-load function
Generator only (no PV, no battery) ✅ Generator starts and stabilizes first, then inverter synchronizes
Generator + Battery ✅ Most robust Most robust option for UK winter

5. Off-Grid Operating Rules

5.1 User Manual

  1. PV power flow priority: load > battery (no export to grid)
  2. PV > load + battery charging capacity: inverter hard-clips PV (MPPT direct limiting, not frequency-shift derating like AC-coupled inverters)
  3. AC-coupled PV inverter (if any): must be configured to "AC coupling" mode + frequency trip value > Solis over-frequency threshold

5.2 Over-Frequency Threshold Settings (50 Hz Grid)

Setting Range Default
Over-frequency trip 50.1 – 54 Hz 51.5 Hz (typical)
Under-frequency trip 46 – 49.9 Hz 47.5 Hz (typical)
  • Why it matters: If the AC-coupled PV inverter is not set to "AC coupling" mode during off-grid operation, it may form a frequency loop with Solis, causing mutual inverter interference and system collapse.

5.3 Off-Grid Power Balance Example

Assumed H125 cabinet configuration:

  • Battery capacity: 261 kWh × 95 % DoD = 247.95 kWh usable
  • Average load: 50 kW (daytime) / 80 kW (night)
  • PV peak: 100 kWp (single inverter supports up to 250 kWp)
  • Battery max discharge: 125 kW (single unit)

Typical daily energy flow:

Time Period PV (kW) Load (kW) Battery (kW) Generator (kW)
06:00–08:00 (early morning) 0 50 +50 (discharge) Off
08:00–12:00 (morning) 30–100 60 -30 → +20 (charge) Off
12:00–14:00 (noon) 100 70 -30 → +20 (charge) Off
14:00–18:00 (afternoon) 30–100 70 -20 → +30 (charge→discharge) Off
18:00–22:00 (evening) 0 80 +80 (discharge) Off
22:00–06:00 (night) 0 50 +50 (discharge) Off when SOC > 30 %
Extreme day (SOC < 20 %) — — +80 +80 (start)

6. Black-Start Hard Limits

6.1 Four Off-Grid Startup Designs That Must Be Avoided

❌ 1. No 100 % Motor-Load Black-Start

  • The backup mode overload curve also applies
  • 125K cannot start 200 kW locked-rotor load from zero
  • Design: Use VFD for large motors, or split into 2 × 125K

❌ 2. No Built-in Transformer

  • Solis 125K generates 230/400 V directly from the battery DC bus via IGBT
  • Not an isolation transformer output
  • Sensitive loads (large UPS / medical equipment) require an external isolation transformer

❌ 3. No PV-Only Battery-less Black-Start

  • Not supported (see §4)
  • Must configure battery or backup generator

❌ 4. No Single-Unit Black-Start (parallel scenario)

  • For multi-unit paralleling, power up Master first, then power up Slaves sequentially (user manual §3.9.7 p.35)
  • Slave will not automatically re-elect a Master

7. Diesel Generator Integration

7.1 Hardware Interface

The inverter exposes 2 DO + 2 DI dry contacts:

Terminal Pins Direction Function
G-S (Generator Start) 11, 12 DO (output) Closed command to START generator
G-V (Generator Valve/Run) 13, 14 DO (output) Closed command for generator RUN / take over load
ATS 5, 6 DI (input) Detect external ATS status (grid trip/close)
ATS-W 7, 8 DI (input) Detect DC 12 V / 5 V adapter grid status signal

7.2 Auto-Start Control Logic

Key fact: The generator is controlled by battery SOC threshold, not grid status.

Setting Range Default Behavior
Generator ON SOC (start) 1 – 95 % 20 % (typical) SOC falls to this value → close G-S → start generator
Generator OFF SOC (stop) 35 – 100 % 80 % (typical) SOC rises to this value → open G-S → stop generator
Generator rated power Manual input — Must equal nameplate kW, used to limit charge current

⚠️ ON SOC must be < OFF SOC (hysteresis); otherwise the generator will cycle on/off. Solis minimum hysteresis = 15 percentage points (e.g., ON = 20 %, OFF = 35 %).

UK winter low-temperature + high-load scenario: recommended hysteresis ≥ 20 % — otherwise the generator may start/stop 5–10 times per day, accelerating wear.

7.3 Three Smart Port Modes

Mode Purpose Trigger Condition
Generator input Diesel / biogas generator mode SOC threshold triggers G-S
Smart load output Drive smart loads (heat pumps, dump loads) PV output exceeds threshold (settable)
AC coupling Connect existing grid-tied PV inverter (retrofit) Manually configure as AC coupling + frequency trip

Typical multi-mode combination: Generator input + smart load output enabled simultaneously (supported by Solis); generate power in off-grid mode, smart load balances PV surplus in grid-tied mode.

7.4 Generator Sizing Rules

Item Limit Note
Capacity (nameplate) No hard upper limit Smart port can connect larger units
Maximum active input 125 kW Hard limit, Smart port will limit current
Recommended capacity range 25 – 125 kW Vendor recommendation
Phase sequence L1↔L1, L2↔L2, L3↔L3 Reverse phase → alarm + generator will not start
Grounding Generator chassis independently grounded + connected to inverter PE bar (not inverter enclosure) User manual p.37 explicit
Grid breaker Must be open (or RCD) when generator is running User manual p.37 explicit
THDv compatibility < 5 % (generator side) Solis requirement

7.5 Sizing Decision Matrix

Load Scenario Recommended Generator Capacity Configuration
Emergency backup (50 % load for 8 h) 50–80 kW ON SOC 30 %, OFF SOC 80 %
Full-load long-term off-grid (125 kW) 125 kW (hard limit) ON SOC 20 %, OFF SOC 90 %
Peak shaving (peak-valley filling) 25–50 kW (daytime valley filling) ON SOC 50 % (start only when SOC is high)
Dual-unit parallel backup 2 × 100 kW ON SOC 25 %, OFF SOC 85 %
UK winter backup 25–50 kW + battery Battery-focused, generator as emergency

8. Generator Start/Stop Signal Chain

8.1 Detailed Step-by-Step Process

Step Action
1 Battery SOC falls below ON threshold (e.g., 20 %)
2 Inverter closes G-S DO contact
3 Generator auto-start input receives start command
4 Generator cranks, runs, reaches rated V/f
5 Inverter detects stable generator via Smart port through ATS / GV feedback
6 Inverter synchronizes to generator, draws up to 125 kW
7 Excess PV (if any) reduces generator load; PV + generator jointly charge battery
8 Battery SOC reaches OFF threshold (e.g., 80 %)
9 Inverter opens G-S DO contact
10 Generator completes cool-down timer (vendor-specific, typically 1–5 minutes) then stops
11 System returns to battery-only or PV-only mode

8.2 Time Budget (Typical)

Phase Duration Cumulative
1–3: Command to START < 100 ms 100 ms
4: Generator crank → stabilization 5–30 s 30 s
5: Feedback to synchronization 1–5 s 35 s
6–7: Synchronize + load pickup 1–5 s 40 s
8–10: Charge to OFF + cool-down 5–30 min 30 min
11: Return to single-battery mode < 1 s 30 min

Total: SOC drops to ON → generator takes over load: ~40 seconds Total: SOC charges to OFF → generator stops: ~5–30 minutes


9. Multi-Unit Paralleling

9.1 Parallel Limit

✅ Up to 10 units Solis 125K can be paralleled with each other (grid-tied + off-grid) 10 × D-Cube-H125/H261 = 1.25 MW AC / 2.61 MWh per site For more than 6 units, Solis STS cabinet is recommended

9.2 Master-Slave Configuration

Item Master Slave
Quantity 1 Up to 9
Function Coordinate PV / battery / load dispatching Receive Master commands
EMS Interface Exposes single Modbus / SolisCloud Pass-through via Master
HV Battery Required Required (1-to-1 pairing)
Slave without battery — Only available when Master's battery is sufficiently large

9.3 Parallel Communication

  • Physical link: P-A, P-B shielded CAT5 cable
  • Shared information:
  • PV voltage / current per MPPT
  • Battery SOC / power
  • Load demand
  • Grid-tied / power intake
  • Dispatch commands (from Master)
  • Topology: Entire cluster = single BESS to upper-layer EMS

9.4 Special Considerations for Off-Grid Paralleling

Item Requirement
Black-start sequence Power up Master first, then power up Slaves sequentially (user manual §3.9.7 p.35)
Communication distance P-A/P-B shielded CAT5 ≤ 100 m (typical)
Synchronization Master-led sync clock
Generator connection Master's Smart port connects to G-S/G-V
ATS ATS / ATS-W connect to Master DI
Fault mode Master offline → Slave will not automatically take over → system shutdown, requires on-site Master restart

11. Common Design Mistakes

  • ❌ Mistake 1: Using the brochure's "2× / 200 ms" directly for motor load design

    Correct: 125K does not support 2×; the upper limit is 1.6× / 200 ms. Designing 200 kW motor load requires splitting into 2 × 125K or using VFD.

  • ❌ Mistake 2: "PV-only, no battery" configuration as a black-start solution

    Correct: The Solis 125K control board is powered from the battery DC bus; PV-only with no battery cannot start. Must configure battery or backup generator.

  • ❌ Mistake 3: SOC threshold ON > OFF or hysteresis < 15 %

    Correct: ON must be < OFF, hysteresis ≥ 15 % (Solis minimum). UK winter recommendation ≥ 20 %. Otherwise the generator cycles on/off, 5–10 times per day, scrap in half a year.

  • ❌ Mistake 4: Generator grounding connected to inverter enclosure

    Correct: User manual p.37 explicit — generator chassis independently grounded + PE bar (not inverter enclosure). Wrong connection causes circulating current, triggers RCD trip.

  • ❌ Mistake 5: Grid breaker not opened when generator is running

    Correct: User manual p.37 explicit — must open the grid-side breaker (or RCD) when the generator is running. Otherwise backfeed to the grid, illegal + safety incident.

  • ❌ Mistake 6: AC-coupled PV inverter not configured to "AC coupling" mode

    Correct: If not configured to AC coupling mode during off-grid operation, may form a frequency loop with Solis, causing system collapse. Must configure AC coupling + frequency trip > Solis over-frequency threshold (50.1–54 Hz).

  • ❌ Mistake 7: Designing PV > 250 kWp (single 125K)

    Correct: DC/AC > 2.0× is not supported, only peak clipping. 250 kWp is the design limit. Customer wants 260 kWp must use 2 × 125K.

  • ❌ Mistake 8: Assuming Slave can automatically take over Master failure

    Correct: When Master is offline, Slave will not automatically take over, system shuts down. Requires on-site manual Master restart, then sequential Slave power-up.

  • ❌ Mistake 9: Using 80K / 100K overload curve for 125K

    Correct: 125K has much weaker overload capability than 80K / 100K. Bidding technical specifications must distinguish. Brochure marketing "2×" applies only to 75–100K.

  • ❌ Mistake 10: In off-grid mode, trying to export all PV output to the grid

    Correct: In off-grid mode, PV priority is load > battery, no export to grid (grid is disconnected, export is impossible). If AC-coupled PV is configured, frequency-shift coordination must be used.


Appendix A: Key Terminology

Term Definition
Black-start Ability to start the system from zero with no external power source
Off-grid mode Operating mode fully disconnected from the grid
Backup mode Grid-storage mutual backup mode (normally grid-tied, automatically switches during outage)
G-S / G-V Generator Start / Generator Valve (DO dry contacts)
ATS / ATS-W Automatic Transfer Switch input
AMF Automatic Mains Failure panel
Smart Port Solis inverter's multi-purpose port (generator / smart load / AC coupling)
SOC threshold control Generator start/stop determined by battery SOC (not grid status)
Frequency-shift AC-coupled PV inverter adjusts output via frequency variation
VFD Variable Frequency Drive (reduces motor startup surge)