D-Cube-H125 / H261 + Solis 125K — Off-Grid / Backup / Generator / Paralleling
Document version: V1.0 (2026-08-26) Scope: BESS selection / bidding / engineering implementation for EU off-grid + backup + generator scenarios Hybrid inverter: Solis S6-EH3P125K10-NV-YD-H (125 kW)
1. Three Off-Grid Application Modes
| Mode | Trigger Condition | Primary Source | Backup Source |
|---|---|---|---|
| Backup (grid-storage mutual backup) | Grid outage | Battery → PV → Generator | — |
| Off-grid (fully islanded) | No grid | PV + Battery + Generator | All |
| Hybrid grid-tied (normal) | Grid normal | PV → Battery / Load / Grid | Battery + Generator |
2. Backup Output — 125 kW Continuous + < 10 ms Transfer
2.1 Key Facts
- 125 kW is continuous rated, not peak
- < 10 ms transfer certified by G99 Type B test (TÜV SÜD report 704092514279-00)
2.2 125K Backup Parameters
| Parameter | Value |
|---|---|
| Backup rated output power | 125 kW |
| Backup rated output current (380 V) | 189.9 A |
| Backup rated output current (400 V) | 180.4 A |
| Rated output voltage | 3/N/PE, 230 V / 400 V |
| THDv (under linear load) | < 2 % |
| Backup transfer time | < 10 ms |
| Maximum phase imbalance | 100 % |
| Maximum single-phase power | 41.66 kW |
| Peak overload (top envelope) | 1.2× 100 s / 1.4× 10 s / 1.6× 200 ms |
| Frequency | 50 Hz / 60 Hz selectable |
2.3 Transfer Time Details
- Grid-tied → Off-grid (grid loss): < 10 ms (automatic)
- Off-grid → Grid-tied (grid restoration): Wait for V/f stabilization, then synchronize (tens of seconds, depending on grid stability)
- PV → Battery: Internal DC-bus transfer, no interruption
- Generator → Battery: Controlled by SOC threshold, see §7
3. Overload Curve
3.1 125K Overload Capability
| Overload Level | 125K | Derating Factor |
|---|---|---|
| 1.2 × (= 150 kW) | 100 s | 6× shorter |
| 1.4 × (= 175 kW) | 10 s | 10× shorter |
| 1.6 × (= 200 kW) | 200 ms | 50× shorter |
3.2 Design Consequences
- ❌ Customer starts 200 kW motor load, single 125K will trip (even at 10 s)
- ❌ Alarm
Over-LoadorOV-ILLC(user manual p.78, 81) - ✅ 125K starting 200 kW locked-rotor load → must split into 2 units
3.3 Design Margin for Key Application Scenarios
| Load Type | Startup Surge | 125K Design Margin |
|---|---|---|
| Resistive (electric heating, incandescent) | 1.0 × | ✅ Sufficient |
| Motor soft-start (VFD) | 1.2–1.4 × / 5–10 s | ✅ OK |
| Motor direct-on-line (DOL) | 5–7 × locked-rotor | ❌ Must use VFD or split units |
| Large transformer inrush | 8–12 × / 100–200 ms | ⚠️ 125K's 1.6×/200 ms may not suffice, on-site test required |
| UPS / PSU capacitor charging | 2–3 × / 50–200 ms | ❌ Not supported (> 1.6×) |
| Welding equipment | 2–5 × | ❌ Not supported |
| Heat pump (compressor startup) | 3–5 × / 200 ms | ⚠️ Use with caution, phased startup required |
4. Black-Start Matrix
4.1 Comparison of 5 Startup Sources
| Startup Source | Black-start Supported | Condition |
|---|---|---|
| PV + Battery | ✅ Recommended | Standard self-consumption sequence |
| Battery only (no PV) | ✅ | SOC ≥ 5–10 % (defined by battery vendor) |
| PV only (no battery) | ✅ | Enable PV-only-load function |
| Generator only (no PV, no battery) | ✅ | Generator starts and stabilizes first, then inverter synchronizes |
| Generator + Battery | ✅ Most robust | Most robust option for UK winter |
5. Off-Grid Operating Rules
5.1 User Manual
- PV power flow priority: load > battery (no export to grid)
- PV > load + battery charging capacity: inverter hard-clips PV (MPPT direct limiting, not frequency-shift derating like AC-coupled inverters)
- AC-coupled PV inverter (if any): must be configured to "AC coupling" mode + frequency trip value > Solis over-frequency threshold
5.2 Over-Frequency Threshold Settings (50 Hz Grid)
| Setting | Range | Default |
|---|---|---|
| Over-frequency trip | 50.1 – 54 Hz | 51.5 Hz (typical) |
| Under-frequency trip | 46 – 49.9 Hz | 47.5 Hz (typical) |
- Why it matters: If the AC-coupled PV inverter is not set to "AC coupling" mode during off-grid operation, it may form a frequency loop with Solis, causing mutual inverter interference and system collapse.
5.3 Off-Grid Power Balance Example
Assumed H125 cabinet configuration:
- Battery capacity: 261 kWh × 95 % DoD = 247.95 kWh usable
- Average load: 50 kW (daytime) / 80 kW (night)
- PV peak: 100 kWp (single inverter supports up to 250 kWp)
- Battery max discharge: 125 kW (single unit)
Typical daily energy flow:
| Time Period | PV (kW) | Load (kW) | Battery (kW) | Generator (kW) |
|---|---|---|---|---|
| 06:00–08:00 (early morning) | 0 | 50 | +50 (discharge) | Off |
| 08:00–12:00 (morning) | 30–100 | 60 | -30 → +20 (charge) | Off |
| 12:00–14:00 (noon) | 100 | 70 | -30 → +20 (charge) | Off |
| 14:00–18:00 (afternoon) | 30–100 | 70 | -20 → +30 (charge→discharge) | Off |
| 18:00–22:00 (evening) | 0 | 80 | +80 (discharge) | Off |
| 22:00–06:00 (night) | 0 | 50 | +50 (discharge) | Off when SOC > 30 % |
| Extreme day (SOC < 20 %) | — | — | +80 | +80 (start) |
6. Black-Start Hard Limits
6.1 Four Off-Grid Startup Designs That Must Be Avoided
❌ 1. No 100 % Motor-Load Black-Start
- The backup mode overload curve also applies
- 125K cannot start 200 kW locked-rotor load from zero
- Design: Use VFD for large motors, or split into 2 × 125K
❌ 2. No Built-in Transformer
- Solis 125K generates 230/400 V directly from the battery DC bus via IGBT
- Not an isolation transformer output
- Sensitive loads (large UPS / medical equipment) require an external isolation transformer
❌ 3. No PV-Only Battery-less Black-Start
- Not supported (see §4)
- Must configure battery or backup generator
❌ 4. No Single-Unit Black-Start (parallel scenario)
- For multi-unit paralleling, power up Master first, then power up Slaves sequentially (user manual §3.9.7 p.35)
- Slave will not automatically re-elect a Master
7. Diesel Generator Integration
7.1 Hardware Interface
The inverter exposes 2 DO + 2 DI dry contacts:
| Terminal | Pins | Direction | Function |
|---|---|---|---|
| G-S (Generator Start) | 11, 12 | DO (output) | Closed command to START generator |
| G-V (Generator Valve/Run) | 13, 14 | DO (output) | Closed command for generator RUN / take over load |
| ATS | 5, 6 | DI (input) | Detect external ATS status (grid trip/close) |
| ATS-W | 7, 8 | DI (input) | Detect DC 12 V / 5 V adapter grid status signal |
7.2 Auto-Start Control Logic
Key fact: The generator is controlled by battery SOC threshold, not grid status.
| Setting | Range | Default | Behavior |
|---|---|---|---|
| Generator ON SOC (start) | 1 – 95 % | 20 % (typical) | SOC falls to this value → close G-S → start generator |
| Generator OFF SOC (stop) | 35 – 100 % | 80 % (typical) | SOC rises to this value → open G-S → stop generator |
| Generator rated power | Manual input | — | Must equal nameplate kW, used to limit charge current |
⚠️ ON SOC must be < OFF SOC (hysteresis); otherwise the generator will cycle on/off. Solis minimum hysteresis = 15 percentage points (e.g., ON = 20 %, OFF = 35 %).
UK winter low-temperature + high-load scenario: recommended hysteresis ≥ 20 % — otherwise the generator may start/stop 5–10 times per day, accelerating wear.
7.3 Three Smart Port Modes
| Mode | Purpose | Trigger Condition |
|---|---|---|
| Generator input | Diesel / biogas generator mode | SOC threshold triggers G-S |
| Smart load output | Drive smart loads (heat pumps, dump loads) | PV output exceeds threshold (settable) |
| AC coupling | Connect existing grid-tied PV inverter (retrofit) | Manually configure as AC coupling + frequency trip |
Typical multi-mode combination: Generator input + smart load output enabled simultaneously (supported by Solis); generate power in off-grid mode, smart load balances PV surplus in grid-tied mode.
7.4 Generator Sizing Rules
| Item | Limit | Note |
|---|---|---|
| Capacity (nameplate) | No hard upper limit | Smart port can connect larger units |
| Maximum active input | 125 kW | Hard limit, Smart port will limit current |
| Recommended capacity range | 25 – 125 kW | Vendor recommendation |
| Phase sequence | L1↔L1, L2↔L2, L3↔L3 | Reverse phase → alarm + generator will not start |
| Grounding | Generator chassis independently grounded + connected to inverter PE bar (not inverter enclosure) | User manual p.37 explicit |
| Grid breaker | Must be open (or RCD) when generator is running | User manual p.37 explicit |
| THDv compatibility | < 5 % (generator side) | Solis requirement |
7.5 Sizing Decision Matrix
| Load Scenario | Recommended Generator Capacity | Configuration |
|---|---|---|
| Emergency backup (50 % load for 8 h) | 50–80 kW | ON SOC 30 %, OFF SOC 80 % |
| Full-load long-term off-grid (125 kW) | 125 kW (hard limit) | ON SOC 20 %, OFF SOC 90 % |
| Peak shaving (peak-valley filling) | 25–50 kW (daytime valley filling) | ON SOC 50 % (start only when SOC is high) |
| Dual-unit parallel backup | 2 × 100 kW | ON SOC 25 %, OFF SOC 85 % |
| UK winter backup | 25–50 kW + battery | Battery-focused, generator as emergency |
8. Generator Start/Stop Signal Chain
8.1 Detailed Step-by-Step Process
| Step | Action |
|---|---|
| 1 | Battery SOC falls below ON threshold (e.g., 20 %) |
| 2 | Inverter closes G-S DO contact |
| 3 | Generator auto-start input receives start command |
| 4 | Generator cranks, runs, reaches rated V/f |
| 5 | Inverter detects stable generator via Smart port through ATS / GV feedback |
| 6 | Inverter synchronizes to generator, draws up to 125 kW |
| 7 | Excess PV (if any) reduces generator load; PV + generator jointly charge battery |
| 8 | Battery SOC reaches OFF threshold (e.g., 80 %) |
| 9 | Inverter opens G-S DO contact |
| 10 | Generator completes cool-down timer (vendor-specific, typically 1–5 minutes) then stops |
| 11 | System returns to battery-only or PV-only mode |
8.2 Time Budget (Typical)
| Phase | Duration | Cumulative |
|---|---|---|
| 1–3: Command to START | < 100 ms | 100 ms |
| 4: Generator crank → stabilization | 5–30 s | 30 s |
| 5: Feedback to synchronization | 1–5 s | 35 s |
| 6–7: Synchronize + load pickup | 1–5 s | 40 s |
| 8–10: Charge to OFF + cool-down | 5–30 min | 30 min |
| 11: Return to single-battery mode | < 1 s | 30 min |
Total: SOC drops to ON → generator takes over load: ~40 seconds Total: SOC charges to OFF → generator stops: ~5–30 minutes
9. Multi-Unit Paralleling
9.1 Parallel Limit
✅ Up to 10 units Solis 125K can be paralleled with each other (grid-tied + off-grid) 10 × D-Cube-H125/H261 = 1.25 MW AC / 2.61 MWh per site For more than 6 units, Solis STS cabinet is recommended
9.2 Master-Slave Configuration
| Item | Master | Slave |
|---|---|---|
| Quantity | 1 | Up to 9 |
| Function | Coordinate PV / battery / load dispatching | Receive Master commands |
| EMS Interface | Exposes single Modbus / SolisCloud | Pass-through via Master |
| HV Battery | Required | Required (1-to-1 pairing) |
| Slave without battery | — | Only available when Master's battery is sufficiently large |
9.3 Parallel Communication
- Physical link: P-A, P-B shielded CAT5 cable
- Shared information:
- PV voltage / current per MPPT
- Battery SOC / power
- Load demand
- Grid-tied / power intake
- Dispatch commands (from Master)
- Topology: Entire cluster = single BESS to upper-layer EMS
9.4 Special Considerations for Off-Grid Paralleling
| Item | Requirement |
|---|---|
| Black-start sequence | Power up Master first, then power up Slaves sequentially (user manual §3.9.7 p.35) |
| Communication distance | P-A/P-B shielded CAT5 ≤ 100 m (typical) |
| Synchronization | Master-led sync clock |
| Generator connection | Master's Smart port connects to G-S/G-V |
| ATS | ATS / ATS-W connect to Master DI |
| Fault mode | Master offline → Slave will not automatically take over → system shutdown, requires on-site Master restart |
11. Common Design Mistakes
-
❌ Mistake 1: Using the brochure's "2× / 200 ms" directly for motor load design
Correct: 125K does not support 2×; the upper limit is 1.6× / 200 ms. Designing 200 kW motor load requires splitting into 2 × 125K or using VFD.
-
❌ Mistake 2: "PV-only, no battery" configuration as a black-start solution
Correct: The Solis 125K control board is powered from the battery DC bus; PV-only with no battery cannot start. Must configure battery or backup generator.
-
❌ Mistake 3: SOC threshold ON > OFF or hysteresis < 15 %
Correct: ON must be < OFF, hysteresis ≥ 15 % (Solis minimum). UK winter recommendation ≥ 20 %. Otherwise the generator cycles on/off, 5–10 times per day, scrap in half a year.
-
❌ Mistake 4: Generator grounding connected to inverter enclosure
Correct: User manual p.37 explicit — generator chassis independently grounded + PE bar (not inverter enclosure). Wrong connection causes circulating current, triggers RCD trip.
-
❌ Mistake 5: Grid breaker not opened when generator is running
Correct: User manual p.37 explicit — must open the grid-side breaker (or RCD) when the generator is running. Otherwise backfeed to the grid, illegal + safety incident.
-
❌ Mistake 6: AC-coupled PV inverter not configured to "AC coupling" mode
Correct: If not configured to AC coupling mode during off-grid operation, may form a frequency loop with Solis, causing system collapse. Must configure AC coupling + frequency trip > Solis over-frequency threshold (50.1–54 Hz).
-
❌ Mistake 7: Designing PV > 250 kWp (single 125K)
Correct: DC/AC > 2.0× is not supported, only peak clipping. 250 kWp is the design limit. Customer wants 260 kWp must use 2 × 125K.
-
❌ Mistake 8: Assuming Slave can automatically take over Master failure
Correct: When Master is offline, Slave will not automatically take over, system shuts down. Requires on-site manual Master restart, then sequential Slave power-up.
-
❌ Mistake 9: Using 80K / 100K overload curve for 125K
Correct: 125K has much weaker overload capability than 80K / 100K. Bidding technical specifications must distinguish. Brochure marketing "2×" applies only to 75–100K.
-
❌ Mistake 10: In off-grid mode, trying to export all PV output to the grid
Correct: In off-grid mode, PV priority is load > battery, no export to grid (grid is disconnected, export is impossible). If AC-coupled PV is configured, frequency-shift coordination must be used.
Appendix A: Key Terminology
| Term | Definition |
|---|---|
| Black-start | Ability to start the system from zero with no external power source |
| Off-grid mode | Operating mode fully disconnected from the grid |
| Backup mode | Grid-storage mutual backup mode (normally grid-tied, automatically switches during outage) |
| G-S / G-V | Generator Start / Generator Valve (DO dry contacts) |
| ATS / ATS-W | Automatic Transfer Switch input |
| AMF | Automatic Mains Failure panel |
| Smart Port | Solis inverter's multi-purpose port (generator / smart load / AC coupling) |
| SOC threshold control | Generator start/stop determined by battery SOC (not grid status) |
| Frequency-shift | AC-coupled PV inverter adjusts output via frequency variation |
| VFD | Variable Frequency Drive (reduces motor startup surge) |