C&I BESS System Efficiency & Auxiliary Power Consumption

This report targets the 125 kW / 261 kWh C&I energy storage cabinet and analyzes the energy link of a complete DOD 0% → 95% → 0% cycle. The system's nominal AC-AC RTE is 88.5%, which — beyond PCS efficiency and battery DC round-trip efficiency — must further deduct the auxiliary consumption of the liquid-cooling unit, BMS/EMS, and dehumidifier.

  • Core RTE (PCS + battery, excluding auxiliary): 88.95%
  • Liquid-cooling electricity consumption per cycle at rated cooling duty cycle: approx. 5.8 – 8.1 kWh (covering the >50% duty-cycle range up to maximum power)
  • Corresponding system net RTE range: 85.15% – 87.48% (from 25% cooling to rated cooling, covering typical on-site operating conditions)

1. System Parameters

Parameter Value Unit
Rated power 125 kW
Rated capacity 261 kWh
Depth of discharge 95 %
Usable battery energy 247.95 kWh
PCS charging efficiency 97.3 %
PCS discharging efficiency 97.3 %
Battery DC round-trip efficiency 94.0 %
BMS+EMS power <200 W
Dehumidifier power 60 W
Fixed auxiliary power 260 W

2. Wiring and Terminals

This section does not involve external wiring; the focus is on energy metering points, with the following suggestions:

  • Grid-side metering: bidirectional meter at the output terminal of the cabinet's grid-connection switch, used as the statistical source for Egrid_inE_{\text{grid\_in}} / Egrid_outE_{\text{grid\_out}}.
  • PCS AC-side metering: bidirectional meter at the PCS AC output port, used to verify PCS internal efficiency.
  • Battery DC side: BMS DC-bus sampling, used to calculate battery DC round-trip efficiency.

Warning

The liquid-cooling unit and dehumidifier are continuously energized equipment. Before maintenance, the upstream circuit breaker must be disconnected and lockout/tagout applied to avoid electric shock or equipment damage from live work.

3. Liquid-Cooling Unit Specifications

Parameter EMW50HFNC1A Unit
Cooling capacity 5.0 kW
Cooling electrical input 2.50 kW
Heating electrical input 2.35 kW
Self-circulating electrical input 0.25 kW
Maximum electrical input 3.60 kW
Circulation flow rate 46.5 @ 60 kPa L/min
Operating voltage 220–240 / 50–60 V/Hz

The unit adopts an inverter compressor + inverter circulation water pump. The master control signal is individual cell temperature (Tmax⁡T_{\max} / Tmin⁡T_{\min}); the setpoint signal is outlet temperature (ToutletT_{\text{outlet}}, configurable via BMS).

3.1 Operating Mode Control Logic (BMS active)

Mode Start Condition Stop Condition Outlet Temperature Setpoint Notes
Cooling Tmax⁡≥33 °CT_{\max} \geq 33\,°C Tmax⁡<30 °CT_{\max} < 30\,°C 22 °C (configurable) Hysteresis 3 °C
Heating Tmin⁡≤10 °CT_{\min} \leq 10\,°C Tmin⁡≥15 °CT_{\min} \geq 15\,°C 20 °C (configurable) Hysteresis 5 °C
Self-circulating ΔT≥4 °C\Delta T \geq 4\,°C ΔT≤2 °C\Delta T \leq 2\,°C — Water pump only, 0.25 kW

Note: Tmax⁡T_{\max} / Tmin⁡T_{\min} are the maximum/minimum individual cell temperatures inside the DC cabinet; ΔT\Delta T is the temperature difference between the inlet and outlet coolant.

3.2 BMS Power-Loss Protection Logic (BMS inactive)

When power is lost, the cooling/heating logic above is retained, with two additional forced self-circulation protections added:

Mode Start Condition Duration Trigger Purpose
Forced self-circulation (high temp) Toutlet≥38 °CT_{\text{outlet}} \geq 38\,°C 120 s Prevent cell overheating
Forced self-circulation (low temp) Toutlet≤8 °CT_{\text{outlet}} \leq 8\,°C 120 s Prevent line condensation/icing

3.3 Mode Priority

Cooling > Heating > Self-circulating; self-circulating can be directly overridden by the forced conditions in 3.2.

4. Communication

This report does not cover external communication protocols, but recommends unifying the following interfaces and data points during on-site data acquisition to facilitate RTE calculation at the upper-level EMS:

  • BMS → EMS: battery DC voltage/current, SOC, SOH, individual cell temperature.
  • PCS → EMS: AC-side voltage/current/power, charge/discharge status, fault word.
  • Liquid-cooling unit → EMS: outlet temperature, compressor/water pump on/off status, current mode (cooling/heating/self-circulating).

Tip

The "cooling/heating/self-circulating" status word of the liquid-cooling unit must be reported to the EMS; otherwise the RTE calculation cannot distinguish between self-circulating and cooling duty cycles, causing a deviation exceeding 1 percentage point.

5. Operating Procedure and Calculation Basis

  • Battery DC round-trip efficiency 94%, symmetrically split into 96.95% × 96.95%
  • PCS charging/discharging efficiency both 97.3%
  • DoD = 95%

Eusable=261×95%=247.95 kWh E_{\text{usable}} = 261 \times 95\% = 247.95 \text{ kWh}

Egrid_in_basic=EusableηDC-AC×ηAC-AC=247.950.973×0.9695=262.84 kWh E_{\text{grid\_in\_basic}} = \frac{E_{\text{usable}}}{\eta_{\text{DC-AC}} \times \eta_{\text{AC-AC}}} = \frac{247.95}{0.973 \times 0.9695} = 262.84 \text{ kWh}

EAC_gross=Eusable×ηAC-AC×ηDC-AC=247.95×0.9695×0.973=233.91 kWh E_{\text{AC\_gross}} = E_{\text{usable}} \times \eta_{\text{AC-AC}} \times \eta_{\text{DC-AC}} = 247.95 \times 0.9695 \times 0.973 = 233.91 \text{ kWh}

Theoretical system efficiency (PCS + battery core, excluding liquid cooling and fixed auxiliary consumption):

ηcore=ηDC-AC×ηbat_RT×ηAC-AC=0.973×0.94×0.973=88.95% \eta_{\text{core}} = \eta_{\text{DC-AC}} \times \eta_{\text{bat\_RT}} \times \eta_{\text{AC-AC}} = 0.973 \times 0.94 \times 0.973 = 88.95\%

  • Charging path: grid → PCS (×97.3%) → battery DC (×96.95%) → stored 247.95 kWh.
  • Discharging path: battery DC (×96.95%) → PCS (×97.3%) → AC gross output 233.91 kWh.
  • Liquid-cooling and auxiliary consumption are presented as a floating branch: auxiliary consumption is added on the charging side, and deducted from PCS gross output on the discharging side.

5.3 General Formula

Let cooling duty cycle be δ\delta (self-circulating duty cycle 1−δ1-\delta); for a single full-power cycle the charging time Tch=Egrid_in_basic/Prated=2.103 hT_{\text{ch}} = E_{\text{grid\_in\_basic}} / P_{\text{rated}} = 2.103 \text{ h}, and the discharging time Tdis=EAC_gross/Prated=1.871 hT_{\text{dis}} = E_{\text{AC\_gross}} / P_{\text{rated}} = 1.871 \text{ h}.

Pliq_avg=Pliq,idle+kcool⋅δ=0.25+2.25δ(kW) P_{\text{liq\_avg}} = P_{\text{liq,idle}} + k_{\text{cool}} \cdot \delta = 0.25 + 2.25\delta \quad \text{(kW)}

Egrid_in=Egrid_in_basic+Tch⋅(Pliq_avg+Paux_fixed)=262.84+2.103⋅(Pliq_avg+0.26)(kWh) E_{\text{grid\_in}} = E_{\text{grid\_in\_basic}} + T_{\text{ch}} \cdot \left( P_{\text{liq\_avg}} + P_{\text{aux\_fixed}} \right) = 262.84 + 2.103 \cdot \left( P_{\text{liq\_avg}} + 0.26 \right) \quad \text{(kWh)}

Egrid_out=EAC_gross−Tdis⋅(Pliq_avg+Paux_fixed)=233.91−1.871⋅(Pliq_avg+0.26)(kWh) E_{\text{grid\_out}} = E_{\text{AC\_gross}} - T_{\text{dis}} \cdot \left( P_{\text{liq\_avg}} + P_{\text{aux\_fixed}} \right) = 233.91 - 1.871 \cdot \left( P_{\text{liq\_avg}} + 0.26 \right) \quad \text{(kWh)}

ηRTE_net=Egrid_outEgrid_in \eta_{\text{RTE\_net}} = \frac{E_{\text{grid\_out}}}{E_{\text{grid\_in}}}

Closed form after substitution (eliminating the intermediate variable Pliq_avgP_{\text{liq\_avg}}):

Egrid_in(δ)=262.84+2.103⋅(0.25+2.25δ+0.26)=263.91+4.732 δ(kWh) E_{\text{grid\_in}}(\delta) = 262.84 + 2.103 \cdot (0.25 + 2.25\delta + 0.26) = 263.91 + 4.732\,\delta \quad \text{(kWh)}

Egrid_out(δ)=233.91−1.871⋅(0.25+2.25δ+0.26)=232.96−4.210 δ(kWh) E_{\text{grid\_out}}(\delta) = 233.91 - 1.871 \cdot (0.25 + 2.25\delta + 0.26) = 232.96 - 4.210\,\delta \quad \text{(kWh)}

ηRTE_net(δ)=232.96−4.210 δ263.91+4.732 δ \eta_{\text{RTE\_net}}(\delta) = \frac{232.96 - 4.210\,\delta}{263.91 + 4.732\,\delta}

5.4 Auxiliary Consumption Scenarios

Fixed auxiliary consumption: BMS + EMS = 200 W, dehumidifier = 60 W (continuously running), totaling Paux_fixed=260 WP_{\text{aux\_fixed}} = 260 \text{ W}. The liquid-cooling unit is modeled under 8 typical states:

Liquid-Cooling State PliqP_{\text{liq}} (kW) PauxP_{\text{aux}} (kW) Eaux_chE_{\text{aux\_ch}} (kWh) Egrid_inE_{\text{grid\_in}} (kWh) Eaux_disE_{\text{aux\_dis}} (kWh) Egrid_outE_{\text{grid\_out}} (kWh) RTE (%)
Liquid cooling off 0.00 0.26 0.55 263.39 0.49 233.42 88.62
Self-circulating [1] 0.25 0.51 1.07 263.91 0.95 232.96 88.27
25% cooling 0.8125 1.0725 2.26 265.10 2.01 231.90 87.48
50% cooling 1.375 1.635 3.44 266.28 3.06 230.85 86.70
75% cooling 1.9375 2.1975 4.62 267.46 4.11 229.80 85.92
Rated cooling 2.50 2.76 5.80 268.64 5.16 228.75 85.15
Rated heating 2.35 2.61 5.49 268.33 4.88 229.03 85.35
Maximum power 3.60 3.86 8.12 270.96 7.22 226.69 83.66

[1] Self-circulating trigger conditions: starts at inlet/outlet coolant temperature difference ΔT≥4 °C\Delta T \geq 4\,°C, stops at ΔT≤2 °C\Delta T \leq 2\,°C. When the battery is idle and the temperature difference is small, the liquid cooling is effectively in the "off" row (0 kW); during charging/discharging or temperature rise, it enters the "self-circulating" row (0.25 kW). If the BMS loses power and outlet Toutlet≥38 °CT_{\text{outlet}} \geq 38\,°C or ≤8 °C\leq 8\,°C, it enters forced self-circulation for 120 s.

5.5 Conclusions and Recommendations

  • Core RTE 88.95%; with 260 W fixed auxiliary, net RTE is approx. 88.6%; drops to 88.27% during liquid-cooling self-circulation; 86.70% at 50% cooling duty cycle.
  • To guarantee the system-level 88.5% nominal RTE, from ηRTE_net≥0.885\eta_{\text{RTE\_net}} \geq 0.885, back-calculating yields:

    Pliq_avg+Paux_fixed≤0.348 kW  ⇒  Pliq_avg≤0.088 kW P_{\text{liq\_avg}} + P_{\text{aux\_fixed}} \leq 0.348 \text{ kW} \;\Rightarrow\; P_{\text{liq\_avg}} \leq 0.088 \text{ kW}

    That is, the combined average power of liquid cooling + fixed auxiliary per cycle must be ≤ 0.35 kW (of which the liquid-cooling unit itself ≤ 0.09 kW, essentially in the off or near self-circulating range).
  • Footnote on self-circulation: per the control logic in Section 3.1, self-circulating starts only when ΔT≥4 °C\Delta T \geq 4\,°C and is not always on. When the battery is idle with a small temperature difference, it is effectively "liquid cooling off" (0 kW) and the RTE can reach 88.62%; during charging/discharging with temperature rise it enters self-circulating (0.25 kW), giving an RTE of approx. 88.27%. The ≤ 0.09 kW control target above does not hold during BMS power-loss forced self-circulation (120 s boundary protection).

Warning

Do not use the "core RTE 88.95%" given in this report directly as the on-site acceptance basis. On-site actual RTE must use bidirectional meter readings on the grid side + PCS AC side, and after deducting auxiliary consumption per the formulas in this report, then compare — otherwise systematic deviation will occur.

Tip

If the site is in rated cooling or higher duty cycle for extended periods (e.g. above 50%), it is recommended to separately negotiate an "RTE including liquid cooling" clause in the commercial/technical agreement to avoid disputes from confusion with the factory-rated 88.5% nominal value.

6. Cautions

  1. The energy link in this report assumes symmetric charge/discharge efficiency. If the on-site PCS efficiency varies significantly across different SOC/power segments, it should be re-fitted piecewise.
  2. The liquid-cooling unit's cooling/heating duty cycles differ significantly at different ambient temperatures; RTE should be calculated within the agreed temperature range.
  3. If the dehumidifier runs on demand rather than continuously at 60 W, replace the fixed term in the formula with the actual duty cycle.
  4. After battery aging, DC round-trip efficiency declines; the RTE calculation should simultaneously introduce an SOH correction factor.
  5. All power/energy values are statistics for a single cycle and cannot be directly extrapolated to daily/monthly data.

Appendix A Symbol Definitions

A.1 System Parameters

Symbol Meaning Value / Unit Source
PratedP_{\text{rated}} Rated charge/discharge power of the storage cabinet 125 kW 1
EratedE_{\text{rated}} Rated battery capacity of the storage cabinet 261 kWh 1
$DoD$ Depth of Discharge 0.95 (95%) 1
EusableE_{\text{usable}} Usable battery energy per cycle 247.95 kWh 5.1

A.2 Efficiency and Baseline Energy

Symbol Meaning Value / Unit Source
ηDC-AC\eta_{\text{DC-AC}} PCS bidirectional inverter efficiency (symmetric charge/discharge) 0.973 (97.3%) 1
ηbat_RT\eta_{\text{bat\_RT}} Battery DC round-trip efficiency (symmetric) 0.94 (94%) 1
ηAC-AC\eta_{\text{AC-AC}} Transformer/line AC-AC efficiency 0.9695 1, 5.1
ηcore\eta_{\text{core}} Core RTE (PCS + battery, excluding auxiliary) 0.8895 (88.95%) 5.1
Egrid_in_basicE_{\text{grid\_in\_basic}} Baseline grid input energy (excluding auxiliary) 262.84 kWh 5.1
EAC_grossE_{\text{AC\_gross}} Baseline AC gross output energy (excluding auxiliary) 233.91 kWh 5.1

A.3 Time and Auxiliary Power

Symbol Meaning Value / Unit Source
TchT_{\text{ch}} Single full-power charging time Egrid_in_basic/PratedE_{\text{grid\_in\_basic}}/P_{\text{rated}} 2.103 h 5.3
TdisT_{\text{dis}} Single full-power discharging time EAC_gross/PratedE_{\text{AC\_gross}}/P_{\text{rated}} 1.871 h 5.3
Paux_fixedP_{\text{aux\_fixed}} Fixed auxiliary power (BMS+EMS+dehumidifier) 0.26 kW 1, 5.4
PauxP_{\text{aux}} Total auxiliary average power (liquid cooling + fixed auxiliary) kW 5.4

A.4 Liquid-Cooling Unit

Symbol Meaning Value / Unit Source
Pliq,idleP_{\text{liq,idle}} Electrical input of liquid-cooling self-circulating (water pump only) 0.25 kW 3
Pliq,coolP_{\text{liq,cool}} Rated cooling electrical input 2.50 kW 3
Pliq,heatP_{\text{liq,heat}} Rated heating electrical input 2.35 kW 3
Pliq,maxP_{\text{liq,max}} Maximum electrical input of liquid cooling 3.60 kW 3
kcoolk_{\text{cool}} Cooling power slope Pliq,cool−Pliq,idleP_{\text{liq,cool}} - P_{\text{liq,idle}} 2.25 kW 5.3
δ\delta Cooling duty cycle 0 ~ 1 5.3
1−δ1-\delta Self-circulating duty cycle 0 ~ 1 5.3
Pliq_avgP_{\text{liq\_avg}} Liquid-cooling average power per cycle kW 5.3
PliqP_{\text{liq}} Liquid-cooling instantaneous power (scenario table) kW 5.4
Tmax⁡T_{\max} Maximum individual cell temperature in DC cabinet (cooling master control signal) °C 3.1
Tmin⁡T_{\min} Minimum individual cell temperature in DC cabinet (heating master control signal) °C 3.1
ToutletT_{\text{outlet}} Liquid-cooling outlet temperature (setpoint/protection signal) °C 3.1, 3.2
ΔT\Delta T Inlet/outlet coolant temperature difference (self-circulating trigger signal) °C 3.1

A.5 Energy and System-Level RTE

Symbol Meaning Value / Unit Source
Egrid_inE_{\text{grid\_in}} Grid input energy including auxiliary kWh 5.3
Egrid_outE_{\text{grid\_out}} Grid output energy including auxiliary kWh 5.3
Eaux_chE_{\text{aux\_ch}} Total auxiliary consumption during charging Tch⋅PauxT_{\text{ch}} \cdot P_{\text{aux}} kWh 5.4
Eaux_disE_{\text{aux\_dis}} Total auxiliary consumption during discharging Tdis⋅PauxT_{\text{dis}} \cdot P_{\text{aux}} kWh 5.4
ηRTE_net\eta_{\text{RTE\_net}} System-level net RTE (including liquid cooling + fixed auxiliary) % 5.3

A.6 Symbol Naming Conventions

  • Subscript in / out indicates energy flowing into/out of the grid.
  • Subscript ch / dis indicates the charging/discharging process.
  • Subscript aux indicates auxiliary systems; subscript liq indicates liquid cooling.
  • Subscript idle / cool / heat / max indicates the liquid-cooling operating tier.
  • Bare subscript max / min indicates the maximum/minimum individual cell temperature (not the power tier).
  • Greek letter η\eta denotes efficiency, δ\delta denotes duty cycle (note: distinguish from DoD), Δ\Delta denotes difference.