Skip to content

Upper Computer MonitorParameter Operation Manual

Part 1 General Description

1. Introduction

1.1 Hardware Interface

1.1.1 D-Cube-A Series Hardware Interface Debugging Connection Method

A Windows laptop is required. Use an Ethernet cable to connect to any LAN port of the switch inside the cabinet.

ScreenShot_2026-09-30_154925_988

1.1.2 D-Cube-S125/261-EU Hardware Interface Debugging Connection Method:

A Windows laptop is required. Use an Ethernet cable to connect to the ETH port on the front panel of the PCS inside the cabinet.

ScreenShot_2026-09-30_155323_941
ScreenShot_2026-09-30_153630_852

1.1.3 D-Cube-F215/418 Hardware Interface Debugging Connection Method

A Windows laptop is required. Use an Ethernet cable to connect to any LAN port of the switch inside the cabinet.

ScreenShot_2026-09-30_160708_111
ScreenShot_2026-09-30_160616_300

1.2 Left Side Function Area

MonitorParameter is used for operation monitoring, data acquisition, parameter configuration, and troubleshooting of Enjoy Technology Co., Ltd power electronics equipment. It supports Modbus TCP, Modbus Uart, and other communication methods, and is applicable to equipment commissioning and operation status management.


2. Software Interface Description

2.1 Left Function Area

Figure: Software Main Interface: Left Function Area

ScreenShot_2026-09-30_163204_350

2.1.1 Communication Settings

Field Description Example
Serial Port Select the serial port for connecting the device COM4
Baud Rate Set the communication baud rate 9600
Parity Select the communication parity mode None
Timeout Set the communication timeout for data packets 800 ms
Device Address Set the Modbus address of the communication device 1
Connection Status Indicates whether the device has been successfully connected Connected

2.1.2 Operation Options

  • Import Watch Items: Import the list of parameters to be monitored via a json file.
  • Export Watch Items: Export the current list of monitored parameters as a json file for easy saving and sharing.

2.1.3 Log Management

  • Communication Log Saving: Records the communication data between the device and the software.
  • Debug Log Saving: Saves debugging information for subsequent problem analysis.

2.2 Right-Side Monitoring Area

2.2.1 Parameter Monitoring Table

ScreenShot_2026-09-30_163529_657
  • Parameter Module: Displays the monitoring data of the device.
Field Description Example
ParameterID Unique identifier of the parameter G 00.32
Parameter Name Specific meaning of the displayed parameter "Year", "Ambient Temperature"
Parameter Value Real-time data returned by the device 27.0 °C
Unit Physical unit of the parameter °C
Display Format Display method of the parameter value Signed Dec
Watch Option When checked, enables focused monitoring of specific parameters Checked

2.2.2 Tab Description

  • PQ Parameters: Displays the real-time parameters related to the device's power quality.
  • Event Records: Records the operating events of the device and supports fault analysis.

2.3 Bottom Status Bar

ui_p06_1
  • Hide Option: Click to hide the left function area; click again to unhide.
  • Communication Status: Displays the current communication method and communication configuration, e.g., Modbus UART: COM4:9600-N-8-1.
Field Description Example
Number of Packets Sent (S) The number of data packets that have been sent 422
Number of Packets Received (R) The number of data packets that have been received 398

The bottom status bar displays the real-time communication operating status of the device.


3. Main Functions

3.1 Communication Settings

Configure the communication port and parameters to establish the connection between the device and the software.

3.1.1 Communication Protocol Selection

Figure: Communication Protocol Selection and En_Uart Driver Installation

ScreenShot_2026-09-30_163915_949

After launching the software, select an appropriate communication protocol as required: ModbusTCP, ModbusUart, or En_Uart.

ui_p07_1

⚠️ Note: The En_Uart protocol requires a dedicated communication tool. Please ensure that the relevant driver has been installed.

ScreenShot_2026-09-30_164113_360
  • Driver installation path: 1-Monitor1129 > EN_Uart+ > CP210xVCPInstaller > CP210xVCPInstaller_x64.exe

3.1.2 TCP Connection Method

Figure: TCP/IP Connection Settings

ui_p08_1

Use a scanning tool to confirm the device's network connection status and IP address: ensure the device communicates properly with the network, and obtain the actual IP address of the device.

ui_p08_2

3.1.3 Connection

Click the Connect button and ensure the communication status displays as "Connected".

ScreenShot_2026-09-30_164513_997

3.2 Model Selection

Figure: Model (Parameter Template) Selection

ScreenShot_2026-09-30_164602_877

After the device type is selected, the software automatically loads the corresponding monitoring parameter template.

💡 Reminder: - PCS English version selection: 9-PCS-EN.xml - Power Quality English version selection: 9-PQ-EN.xml

3.3 Parameter Monitoring

Figure: Parameter Monitoring and Address Display Format

ui_p09_1

Real-time display of device operating parameters, including key data such as temperature and voltage.

💡 Note: Right-click on the ParameterID of any parameter, select the "Address Display Format" option, and set the current parameter ID to hexadecimal to calculate the corresponding register address. This provides convenience for subsequent EMS development, control, and usage.

ui_p10_1

3.4 Event Records

Figure: Event Records

ui_p10_3

View historical events to assist in troubleshooting.

3.5 Clear Monitoring

The "Clear Monitoring" function is used to quickly remove all currently selected monitoring parameters. This function is applicable to scenarios where parameters need to be reconfigured or invalid monitoring items need to be cleared, ensuring that the monitoring interface remains clean and focused.

3.6 Import/Export Observations

Figure: Import/Export Observation Items

ui_p11_2

This feature supports batch import and export operations for commonly used parameters that have been added to observations across different device models. With this feature, users can efficiently share observation parameter configurations between multiple devices, improving operational efficiency and reducing the workload of manual configuration.

Operation Steps:

  1. Click the Import Observation Items button.
ui_p11_4
  1. Select the prepared JSON file (e.g., Key Configuration_STS+PCS.json).
ui_p12_1
  1. After import, the key configuration parameter items will be displayed in the monitoring list on the right side.

4. Precautions

  1. Ensure that the configuration (baud rate, parity bit, etc.) is consistent with the device hardware.
  2. Avoid multiple devices accessing the same serial port simultaneously during operation.
  3. Before parameter configuration, please confirm the parameter range to avoid abnormal device operation.
  4. When using the import function, ensure that the JSON file format is correct.

5. Frequently Asked Questions and Solutions

Issue Possible Cause Solution
Unable to connect to the device Incorrect serial port settings or the device is not powered on Check whether the serial port number, baud rate, and other configurations are correct, and restart the device
Parameter display anomaly Communication interruption or device fault Check the communication lines and ensure the device is operating normally
Unable to import the parameter file Incorrect file format Ensure that the JSON file conforms to the standard format supported by the software
Lag or no response during runtime Insufficient PC performance or excessive data volume Optimize PC performance and reduce the number of monitored parameters
Device cannot be discovered Blocked by firewall Open the firewall in the PC properties and allow the application through the firewall

Part II: Backend Software Operation

The original document of this section is mainly composed of interface screenshots; here it is organized into structured operation steps; locations marked with [Screenshot] are interface diagrams in the original document.

6. Configuration Files

Figure: Configuration Files and Folder Structure

op_p01_1
op_p01_2
  1. The software directory should contain the Config.json file, which includes the paths of the related configuration files.
  2. The Cfg folder should contain the corresponding subfolders. [Screenshot]
  3. The Paralist folder should contain configuration files, such as ParamList_CN.xml, etc. (Place the configuration files under the Paralist folder according to your specific requirements).
  4. Add parameter configuration files for different languages as needed. If a corresponding language file is added, place it in the corresponding folder. [Screenshot]

7. File Integrity Check (First Use)

  • Check whether the obtained folder is complete, especially the cfg folder and the paralist folder, as they relate to key functions.
op_p01_3
  • The Cfg folder should contain the following subfolders
op_p01_4
  • The paralist folder should contain configuration files, for example as follows (depending on your specific needs, place the configuration files under the Paralist folder)
op_p02_1
  • Add parameter configuration files for different languages as required. If a corresponding language file is added, simply place it in the corresponding folder.
op_p02_2
Check Item Description
Config.json Software root directory, records the paths of each configuration file
cfg folder Required for key functions; missing it will cause functional abnormalities
paralist folder Stores parameter configuration files (ParamList_CN.xml / ParamList_EN.xml, etc.)
Language files Placed into the corresponding language subfolder as required

8. INI File Description

8.1 [general] General Configuration

Key Example Value Description
deviceaddr 1 Device address
communicationtype ModbusUart Communication type. The protocol defaults to ModbusTCP, ModbusUart, or En_Uart; any other input defaults to ModbusTCP
timeout 50 Receive timeout
language CN Default language: CN for Chinese, EN for English
Delayms 5 Inter-frame delay time
Logfilefoldermaxsize 512 Maximum size of the log folder
logfilemaxsize 20971520 Maximum size of a single log file
configfilename ParamList_CN.xml Configuration file opened by default
fontgrade 1 Font grade: 0 Small, 1 Medium, 2 Large

8.2 [serialport] Serial Port Configuration

Key Example Value Description
com COM5 Serial port number
baud 9600 Baud rate
parity N Parity: N / E / O
databits 8 Data bits
stopbits 1 Stop bits

8.3 [network] Network Configuration

Key Example Value Description
ip 192.168.1.200 IP address
port 502 Port number

8.4 Original INI Content Example

Figure: INI Configuration File

op_p02_3
[general]
deviceaddr = 1                     /*Device address*/
communicationtype = ModbusUart     /*Communication mode. Protocol defaults to ModbusTCP, ModbusUart, or En_Uart; any other input defaults to ModbusTCP*/
timeout = 50                       /*Reception timeout*/
language = CN                      /*Default language: CN for Chinese, EN for English*/
Delayms = 5                        /*Inter-frame interval*/
Logfilefoldermaxsize = 512         /*Log folder size*/
logfilemaxsize = 20971520          /*Log file size*/
configfilename = ParamList_CN.xml  /*Default configuration file to open*/
fontgrade = 1                      /*Font grade: 0 small, 1 medium, 2 large*/

[serialport]
com = COM5
baud = 9600
parity = N
databits = 8
stopbits = 1

[network]
ip = 192.168.1.200
port = 502

9. Log File Description

9.1 Communication Log Files

Figure: Communication Log Saving

op_p03_1
op_p04_1
op_p04_2
op_p04_3

Check the option to save communication logs; the data is saved in the folder where the software is located, as a txt file named after the current communication port. Click the button on the right to automatically open the saved path.

9.2 Debug Log File

Figure: Debug Log Saving

op_p04_4
op_p05_1

Enable "Debug Log Saving" to save debug logs. This is generally not required.


10. Search IP

op_p05_3

Figure: Search Device - Search IP

op_p05_4
  1. Click Search Device to search.
  2. Double-click the target device in the table, and the IP address will be automatically filled in the IP address field.
  3. Click Connect.
  4. If no device is found, please open the firewall in the computer properties and allow the application through the firewall.

11. PQ Parameters Page

11.1 Reading Data

Click Connect to start reading (when the port is functioning normally); click Disconnect to stop reading.

op_p06_1

11.2 Data Export

Figure: PQ Parameter Export

op_p07_1

Click the popup, select the export file type, enter the file description, select the file path, and confirm to export.

File Type Content Format
Interface Data (.csv) All data on the current interface csv
Interface Data (.json) All data on the current interface json (decimal)
Observation Configuration Data (.json) Data of the currently observed items json (hexadecimal)
op_p07_2

Observation configuration data can be used to import data.

11.3 Data Import

Figure: PQ Parameter Import and Download

op_p08_1
  1. Click Data → Import Data.
  2. Select the configuration file (the file is the "Observation Configuration Data (.json)" file in the exported data).
  3. The table is editable; you can check whether to read or write, and export the current configuration file.
  4. After confirming, click Download Parameters.

11.4 Import Observations

Select a valid observation data file and open it.

11.5 Export Observations

Figure: Export Observations

op_p08_2

Save the observation data of the current interface, which can be imported as observation data for next use.

11.6 Select/Switch Configuration Profile

Figure: Switch Configuration Profile

op_p09_1

Switch the configuration profile and select your own configuration profile.

11.7 Search Parameters

Figure: Search Parameters

op_p09_2

Click Search Parameters, enter the search content, click the search button or press Enter, and right-click to add to the watchlist.

11.8 Switching Language

Figure: Switching Language and Configuration File

op_p09_3

After switching the language, you need to manually switch the XML configuration file: Paramlist_EN.xml is the English version of Paramlist.xml.


12. Event Log Page

Figure: Event Log Page Operations

op_p10_1
  1. Filter Event Type: Filter by event type.
  2. Query Records: Query the records of the existing entry count.
  3. Save Records: Save the event records to the specified location.
  4. Clear Records: Clear the event records.

13. Factory Settings Page

13.1 Downloading Parameters

Select the parameter configuration, or choose a file from the drop-down box, and check the parameters that need to be downloaded.

13.2 Read Parameters

Figure: Factory Settings: Download/Read Parameters

op_p12_1
op_p12_2

Select and check the rows you want to read, then click Read Parameters.

13.3 Clear Status

Clear the status bar in the settings result display box and the table.

op_p13_1

13.4 Reload File

Figure: Reload File and Clear State

op_p13_2

Reload the selected file.

13.5 Specified Commands

Figure: Specified Command and Saving Configuration

op_p14_1

Open-Loop Waveform Output, Parameter Burning (固化参数), and Zero-Drift Calibration are several special commands.

13.6 Save Configuration

op_p14_2

Saved to the selected file.

13.7 Real-Time Save Record

op_p15_1
op_p15_2

To preserve the records, exiting the Factory Settings page saves the records in a txt file.

13.8 Hidden Parameters

Figure: Hidden Parameters

op_p15_3

Hide some unnecessary parameters from display.


14. Real-Time Curve Page

  1. Auto Save: Enable auto save.

Figure: Real-Time Curve: Auto Save and Export

op_p16_1
op_p16_2
  1. Export Data:
op_p17_1
  • Short-duration operation → Select the "Export Data" option;
  • Long-duration operation → Select the "Real-Time Save".

  • Select Channel Color:

Figure: Channel Color and Operation

op_p17_2

Double-click the corresponding channel in the form on the right; a color palette will pop up, where you can choose a custom color. After closing the dialog box, the corresponding channel will change to the custom color background.

  1. Run: Supports single-channel and multi-channel operation.
op_p18_1
op_p18_2
op_p18_3

15. Operation Log Page

  1. Auto Save: Auto-saved under the Log folder.

Figure: Operation Log: Auto Save and Filter

op_p19_1
op_p19_2
op_p19_3
  1. Show Only Success:
op_p20_1

Only successful results are displayed; otherwise, all results are displayed.

  1. Save Log: Select the save path and click Save.
op_p20_2
op_p20_3
  1. Clear Log: Clears the records on the interface.

Figure: Operation Log: Save / Clear / Open

op_p21_1
  1. Open Log: Opens a previously saved log.
op_p22_1
  1. Record Configuration:

Figure: Open Log and Record Configuration

op_p22_2

Fill in the file description and click Save to save the content in the log. This function is used for importing factory configuration files.